If you search Google for "demand load...

If you search Google for "demand load calculation" you'll find some spreadsheets or other online guides to work through the calculation. This exact process is based on the US code, but CEC should be...
01-23-17, 01:35 PM
Replies: 10
Views: 5,428
Posted By ibpooks

The panel needs to have at least the rating of...

The panel needs to have at least the rating of the feeding breaker. For example, you can feed a 125A panel with a 100A breaker.

A main breaker is not required for a subpanel in the same building...
01-23-17, 11:45 AM
Replies: 10
Views: 5,428
Posted By ibpooks

I think the 60A panel would probably be just...

I think the 60A panel would probably be just fine; however a 100A will not cost too much more if you want to go that way. Where is your home's main panel in relation to where you would like to...