03-15-09, 06:56 AM
Replies: 8
Views: 1,745
Posted By pcboss

You might run into a workspace violation...

You might run into a workspace violation depending on the headroom under the beam. You would also need to rerun at least part of the conduits over to the new panel.

If I were doing the job I...
03-05-09, 08:31 AM
Replies: 8
Views: 1,745
Posted By pcboss

A backfed breaker has the power coming in through...

A backfed breaker has the power coming in through the screw terminals instead of the buss conections. The power then goes into the buss. You would keep the main breaker off while backfeeding the...
03-05-09, 07:36 AM
Replies: 8
Views: 1,745
Posted By pcboss

Not that familiar with GE, but I doubt that the...

Not that familiar with GE, but I doubt that the 60 will have the same shape or mounting as a standard main breaker.

You could probably mount a standard 2 pole 60 and attach the wires to it to...