04-27-16, 08:23 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

I did a bit of reading about the differences...

I did a bit of reading about the differences between THWN and XHHW. Course it's the Internet, but, it sounds like XHHW has better outer insulation and I ran across something about THWN installation...
04-27-16, 01:27 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

I'm figuring on #1 XHHW copper since I need the...

I'm figuring on #1 XHHW copper since I need the 130A capacity as I'm using 125Amp Eaton BR2125 breakers.
04-27-16, 12:52 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

I'd prefer to run a ground, I guess it just makes...

I'd prefer to run a ground, I guess it just makes me more comfortable. I'm surprised #8 is all I need! I was expecting only a size or two smaller. #8 is much more wallet friendly! Thanks for the info!
04-27-16, 10:45 AM
Replies: 30
Views: 4,847
Posted By Mark Brewster

I was looking at the SER because it was easy to...

I was looking at the SER because it was easy to get here locally. I see your point though and did some searching around. I think I'll use #1 XHHW copper. What is common practice, and code of course,...
04-25-16, 12:45 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

Started to pick stuff up for the project as...

Started to pick stuff up for the project as budget allows. I grabbed the Eaton 125 amp panel at Lowe's, the one with the 5 20 amp breakers included and 2 of the Eaton 125 amp breakers. I was planning...
04-22-16, 11:50 AM
Replies: 30
Views: 4,847
Posted By Mark Brewster

That is a good idea too. If I upgrade that...

That is a good idea too. If I upgrade that subpanel to 125 amps, would that be enough to service the finished basement circuits as well directly from that subpanel? That subpanel currently has 20...
04-22-16, 09:20 AM
Replies: 30
Views: 4,847
Posted By Mark Brewster

Just stumbled onto a possible option that...

Just stumbled onto a possible option that wouldn't require opening up the drywall. Is there anything wrong with using an Eaton BQC225225 breaker to combine the 2-25amp 2 pole breakers for the 2 air...
04-16-16, 10:20 AM
Replies: 30
Views: 4,847
Posted By Mark Brewster

I'm good with drywall, it's the look on my wife's...

I'm good with drywall, it's the look on my wife's face when I tell her I'm cutting a hole in the pantry in her new house that I'm not crazy about! Actually, putting in an access panel is a good idea...
04-15-16, 08:10 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

Ok, my memory isn't so good. The sub panel is a...

Ok, my memory isn't so good. The sub panel is a 200 amp Eaton. There's no kill switch in the sub panel but there is a 50 amp breaker in the main panel. I can't tell the gauge but each wire is about a...
04-15-16, 07:12 AM
Replies: 30
Views: 4,847
Posted By Mark Brewster

Conduit would be all indoors. I have the ability...

Conduit would be all indoors. I have the ability to go straight into the wall from the panel with existing wires and into the basement, run along floor joists till it pops through into the garage at...
04-14-16, 09:34 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

Of course now I'm thinking about a sub panel in...

Of course now I'm thinking about a sub panel in the garage... I have a 100 amp sub panel next to the main that is almost empty. That is why I hadn't really considered it before. But, im also running...
04-14-16, 08:49 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

I wasn't planning on any wire runs outside, it'll...

I wasn't planning on any wire runs outside, it'll all be inside in conduit. I didn't realize the welder only had a three prong plug as I haven't picked it up yet. Just have it picked out. The camper...
04-14-16, 05:18 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

This is an attached garage and the garage is...

This is an attached garage and the garage is drywalled already. The wall I'm running down is the exterior one, not shared with the house. I can't bury the wire either because the side of the garage...
04-14-16, 03:28 PM
Replies: 30
Views: 4,847
Posted By Mark Brewster

Running 240v 50amp outlet in my garage

Hey guys,

I'm getting ready to run a 240v 50amp outlet in my garage. The purpose of the outlet is to run a Lincoln AC-DC 225 welder and to also plug our camper's 50amp service in. I'll never be...