04-17-14, 01:52 PM
Replies: 11
Views: 1,024
Posted By ray2047

Yes. So long as it is an attached garage you...

Yes. So long as it is an attached garage you don't even need a subpanel. You can run individual cables or a combination of individual and subpanel as you asked about.
04-17-14, 11:36 AM
Replies: 11
Views: 1,024
Posted By ray2047

Than no ground rod or GEC is needed, just an EGC...

Than no ground rod or GEC is needed, just an EGC wire. No disconnect either so no main breaker panel. Just a main lug only.Only if both sets of terminals are rated for 90. Better to use #1...
04-17-14, 11:05 AM
Replies: 11
Views: 1,024
Posted By ray2047

Yes, a separate ground rod for a detached...

Yes, a separate ground rod for a detached structure.Code requires a disconnect if you have space in the panel for more than six circuits. That disconnect must be rated 100 amps or more in your case...