Replies: 17
Views: 1,646
Posted By PJmax

The differential only controls the low limit...

The differential only controls the low limit switch.

Differentials:
High Limit: 10F (6C) nominal. (not adjustable)

High Limit: 130F (55C) to 240F (116C). Stops burner if
boiler...
Replies: 17
Views: 1,646
Posted By PJmax

Are you talking about the low limit on the...

Are you talking about the low limit on the aquastat in the pictures 7 & 8 ?

That low limit adjustment only affects the right side switch.
I posted this previously....
The left side B and R is...
Replies: 17
Views: 1,646
Posted By PJmax

I'm responding to so many threads it's hard to...

I'm responding to so many threads it's hard to keep each one separate.

From the aquastat instructions......
Set the low limit and/or circulator adjustment to obtain temperature desired but not...
Replies: 17
Views: 1,646
Posted By PJmax

pic 4 - custom timer board. No way to modify. ...

pic 4 - custom timer board. No way to modify.
pic 5 & 6 - that's a 24vac controlled relay. Completely bypassed.

pic 7 & 8 - L6081- 1036 aquastat. Wired for high limit to open just the hot of...
Replies: 17
Views: 1,646
Posted By PJmax

If you have problems posting the pics.... send me...

If you have problems posting the pics.... send me a PM and I'll give you my email address. You can send them there and I'll post them for you.
Replies: 17
Views: 1,646
Posted By PJmax

Welcome to the forums. A semi complicated...

Welcome to the forums.

A semi complicated system made more complicated by location.
I don't see any pictures posted. How-to-insert-pictures...