03-20-13, 09:29 AM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

Thanks everyone for your suggestions. I did end...

Thanks everyone for your suggestions. I did end up calling a professional and it turns out that I had plugged the breakers into a delta high leg. I hope I got that name right. Anyway, it was a...
03-19-13, 05:25 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

Between the two mains, it registers over 300...

Between the two mains, it registers over 300 which is the highest value on the meter
03-19-13, 05:19 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

Ground to left = 150 Ground to right = 270 ...

Ground to left = 150
Ground to right = 270
Left to right is more than 300
03-19-13, 04:53 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

I'm pretty sure I'm not reading the wrong scale. ...

I'm pretty sure I'm not reading the wrong scale. The problems are occurring in the guest house. I have tried the meter in my main house and all the readings are within normal range
03-19-13, 04:49 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

I'm putting the probes into the plug. On the 120...

I'm putting the probes into the plug. On the 120 plugs: red in the left, black in the right.

On the 220 outlet, I'm measuring black in the ground and red on either the left or the right hot.
03-19-13, 04:45 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

Oops... 120 outlets. I'm in AZ, USA

Oops... 120 outlets. I'm in AZ, USA
03-19-13, 04:39 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

15 amp breaker with 12/2 wire to the 110 outlets.

15 amp breaker with 12/2 wire to the 110 outlets.
03-19-13, 04:35 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

The two circuits were run separately. I'm using...

The two circuits were run separately. I'm using an analog multimeter.
03-19-13, 04:32 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

I'm taking the readings from each individual...

I'm taking the readings from each individual outlet. Everything s unplugged
03-19-13, 04:25 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

110 outlets pulling 280 volts

Why are my outlets reading 280 volts?
03-19-13, 04:22 PM
Replies: 34
Views: 7,977
Posted By GossieCrewOf4

220 outlet pulling 400 volts

This thread is two similar threads by the same poster that have been combined.

I recently installed a 220 outlet in a new guest house. One side is reading about 140 volts and the other side is...