12-15-14, 08:04 PM
Replies: 12
Views: 972
Posted By Tolyn Ironhand

It is a NEC requirement per 352.10(F) ...

It is a NEC requirement per 352.10(F)

Conduits installed on poles are required to be PVC Sch 80, RMC, IMC, or equivalent. 300.50(C)
12-14-14, 03:18 PM
Replies: 12
Views: 972
Posted By Tolyn Ironhand

If the area where the conduit is to be installed...

If the area where the conduit is to be installed is subject to physical damage (vehicle traffic, weed whips, rambunctious kids, etc.) then Sch 80 is required. Otherwise Sch 40 is fine.
12-13-14, 05:13 PM
Replies: 12
Views: 972
Posted By Tolyn Ironhand

Welcome to the forums! Is sounds to me that...

Welcome to the forums!

Is sounds to me that your pole mounted panel is the main for the property. That would make the house panel a sub panel detached from the main "building". You need 4 wires.