Replies: 8
Views: 5,823
Posted By iceman

We have ignition

Trooper -

I got to thinking about your comment that the problem really wasn't solved by the new valve and to check wiring.

I went back to both sets of the red wire connections, took them apart...
Replies: 8
Views: 5,823
Posted By iceman

A Further Explanation

Trooper --

Thanks for the reply.

What I call the circulator is the box on the boiler, I guess the real term is aquastat.

As far as my set up, you are correct. Two of the three zones operate...
Replies: 8
Views: 5,823
Posted By iceman

Sorry, I don't have a multimeter. I'll get one...

Sorry, I don't have a multimeter. I'll get one if it will help, though I'll probably never use it again.

Is there another test? The zone valve is brand new, so I would hope its not the endswitch...
Replies: 8
Views: 5,823
Posted By iceman

Zone Valve Wiring

I have a three zone heating system with Honeywell valves
(8043E1012).

Two of the zones work well. Recently, the third zone (Z3) didn't seem to be working. I replaced the thermostat, but there...