If the a/c unit draws 8A @ 250V, it will draw 16A...

If the a/c unit draws 8A @ 250V, it will draw 16A @ 125V.

Transformer losses might be 2%, but nowhere near 50%.

The a/c unit might require 50A to start the compressor. So a larger transformer...
04-21-06, 08:30 PM
Replies: 9
Views: 16,477
Posted By bolide

You need a 1:2 3000VA step-up transformer. ...

You need a 1:2 3000VA step-up transformer.
Google (http://www.google.com/search?q=120V+220V+transformer) gave some results that appear promising such as Transformer 3000 VA, 110 V / 230 V...