Replies: 9
Views: 2,833
Posted By bovineu

The boiler loop flow is constant and is run by...

The boiler loop flow is constant and is run by the grundfos 3 speed on low speed.

yes the logic is different with the two pumps and they run differently at least from what I observed.

The...
Replies: 24
Views: 4,782
Posted By bovineu

That is comforting to know that the constant...

That is comforting to know that the constant circulation will not put any additional wear on my system.

And I have one zone right now but have set it up so I can add an additional zone in the...
Replies: 24
Views: 4,782
Posted By bovineu

Downside to constant circulation?

My newly installed boiler is the buderus gb142/24. I also purchased the RC35 controller giving me indoor feedback to the system allowing me to run with constant circulation.

My installer does not...
Replies: 9
Views: 2,833
Posted By bovineu

Thanks for your responses. Jbaron, I think you...

Thanks for your responses. Jbaron, I think you answered my question as far as logic. I will try to get the system flow to be as close to the flow in the boiler loop (15-58) which I think will be the...
Replies: 9
Views: 2,833
Posted By bovineu

I have called Buderus on what they feel the...

I have called Buderus on what they feel the minimum system flow rate should be but the tech guy I spoke with was new and is having someone call me back. Its been a couple of days which is why I...
Replies: 9
Views: 2,833
Posted By bovineu

Just to add some background info, this is a one...

Just to add some background info, this is a one zone system.
Replies: 9
Views: 2,833
Posted By bovineu

Required System Flow to prevent short cycling in Mod/Con

Just had a Buderus GB142/24 installed. My heatloss is 36k BTU @ design so while its the smallest size they make, it is oversized. I realize it will short cycle during shoulder months but would like...