10-06-05, 02:07 PM
Replies: 16
Views: 20,517
Posted By racraft

Well then you donít need a neutral. However, I...

Well then you donít need a neutral. However, I would still run one, since you or someone else may change the tub in the future.
10-06-05, 12:55 PM
Replies: 16
Views: 20,517
Posted By racraft

Use the 6/3 cable to pull the THWN wires. Use...

Use the 6/3 cable to pull the THWN wires. Use wire lubricant on the wires.
10-06-05, 11:46 AM
Replies: 16
Views: 20,517
Posted By racraft

I don't have the info in front of me to verify...

I don't have the info in front of me to verify this right now, but I believe that the ground can be 8 gage.
10-06-05, 11:36 AM
Replies: 16
Views: 20,517
Posted By racraft

Use green for the ground. Use white for the...

Use green for the ground. Use white for the neutral. For the hot wires you can use just about any other color. They can even be the same color if you want. However, I would go with black and red.
10-06-05, 10:27 AM
Replies: 16
Views: 20,517
Posted By racraft

You are not thinking right. The white wire is...

You are not thinking right. The white wire is the neutral needed by the spa.
10-06-05, 09:48 AM
Replies: 16
Views: 20,517
Posted By racraft

Sorry, you were misinformed. the wire outside...

Sorry, you were misinformed. the wire outside MUST be individual conductors. You are not allowed to use something with a bare ground wire outside. The 6/3 has a bare ground wire, so is not...