05-30-20, 05:28 PM
Replies: 6
Views: 250
Posted By PJsDad

Suspecting the transformer then

Thanks so much for your insight on the grouping of the connections on the board. Very helpful.

Based on this I think I will put on a different transformer and bring 24v into the board without...
05-30-20, 06:23 AM
Replies: 6
Views: 250
Posted By PJsDad

I replaced the board and igniter. Trane has gone...

I replaced the board and igniter. Trane has gone to a 120v igniter. the original was 70v. The results with the old board and the new board are identical. Thatís why I was wondering if something...
05-29-20, 05:58 PM
Replies: 6
Views: 250
Posted By PJsDad

Things Iíve tried

Yes, I taped the cover switch and then, in case the switch was defective I continuity tested it.

The board is hot on the 120 side, just nothing coming to the transformer so thereís no 24v control...
05-27-20, 04:45 PM
Replies: 6
Views: 250
Posted By PJsDad

Trane XE80 not sending 120v to transformer

This unit fired up correctly the first couple of times I tried it, but then shut off. I cleaned the flame sensor and from then on the furnace is completely in-active. I put a new flame sensor on it...