Showing results 1 to 15 of 15
Search took 0.01 seconds.
Replies: 10
Views: 817
Posted By stowepotato

I think Spott has hit the spot (arghh......)....

I think Spott has hit the spot (arghh......). Intuitively, I boosted the differential to 20. I thought it helped a little, but still get some short cycles. Of the 4 zones, two are upstairs bedrooms...
Replies: 10
Views: 817
Posted By stowepotato

Set the Hi limit to 190. Watched an entire cycle...

Set the Hi limit to 190. Watched an entire cycle while a thermostat was calling. Boiler temp. started at 172, hit 190, overran to 194 after the burner shut off, dropped back down to 175 (190...
Replies: 10
Views: 817
Posted By stowepotato

Thanks, I see what you're saying now and agree...

Thanks, I see what you're saying now and agree there is some logic to boosting the Hi limit. This I will try. And perhaps later will also increase the differential. I see others who suggest that...
Replies: 10
Views: 817
Posted By stowepotato

Are you suggesting raising the high limit and...

Are you suggesting raising the high limit and increasing the differential? There is no low limit set to maintain a minimum boiler temperature. It only fires on demand, the so-called cold start mode.
Replies: 10
Views: 817
Posted By stowepotato

Thanks. I did try increasing the differential to...

Thanks. I did try increasing the differential to 15 and that had no effect. Set it back to 8 but haven't had time to see any result.
Maybe I should go to 20-25 differential which would allow the...
Replies: 10
Views: 817
Posted By stowepotato

Oil burner short cycling

Crown Boiler, Riello burner, 4 zones, TACO 404 ZVC, one TACO circulator, Honeywell zone valves, external DHW.. L7224U aquastat with Lo limit set to OFF.
I thought that my problem was the 24 year old...
Replies: 13
Views: 922
Posted By stowepotato

Got the L7224U in 2 days from Supply House. I've...

Got the L7224U in 2 days from Supply House. I've bought other items from them before, always with super good service.
Pulled the old L8148A and found it already had thermal grease in the well, so...
Replies: 13
Views: 922
Posted By stowepotato

Thanks Doughness. Replacing the L8148A with a...

Thanks Doughness.
Replacing the L8148A with a newer L7224U is the direction that makes sense to me. I suspect the erratic performance is due to poor contact of the bulb in the well. I have thermal...
Replies: 13
Views: 922
Posted By stowepotato

I had an Intellicon installed and just took it...

I had an Intellicon installed and just took it off. The burner was still short cycling when it was in place and I could see no difference in consumption. Service techs say they have seen most of them...
Replies: 13
Views: 922
Posted By stowepotato

L8148A aquastat

My basic question remains: How is the fixed differential built into this device and do they fail? I don't know where to look for a failure point. Is it a circuit board component, a piece of metal in...
Replies: 13
Views: 922
Posted By stowepotato

I've seen the info on this universal electronic...

I've seen the info on this universal electronic control.
I need to make sure it will fire the boiler only on demand (i.e when one of the thermostats is calling for heat).
I don't want to maintain a...
Replies: 13
Views: 922
Posted By stowepotato

Sometimes it is clear that the boiler temp drops...

Sometimes it is clear that the boiler temp drops down by 8-10 degrees Other times it only drops 1-2 degrees before firing as long as the thermostat is still calling for heat.
Replies: 13
Views: 922
Posted By stowepotato

L8148A aquastat differential failure

While calling for heat and after reaching the 180 high limit, the burner shuts down. Good, that's what it is supposed to do. But then the burner may start again after only dropping a couple of...
Replies: 9
Views: 1,163
Posted By stowepotato

Thanks

Thanks to all who responded to my problem. I conclude that the cause of premature failure is dissolved oxygen from the rubber and/or PVC components. Unfortunately, the rubber tubing is engineered...
Replies: 9
Views: 1,163
Posted By stowepotato

Expansion tank rusting through

I have a closed loop hydronic heating system for my small greenhouse. Heat source is an electric Bosch water heater. System operates at 12 psi and 80-120. Approximately 5 ft of copper piping in the...