Open neutral

I had a similar problem with bathroom lights not working. Check wiring from the nearest outlets. The neutral wire is probably loose. Mine was push in connection that became loose even though it...
06-14-20, 11:53 AM
Replies: 14
Views: 394
Posted By 2john02458

I have marked up your drawing to show the problem...

I have marked up your drawing to show the problem areas and some suggested solutions.

If you decide to use brackets I would advise that they be heavier than the ones usually found in the big box...
04-22-20, 10:24 AM
Replies: 5
Views: 219
Posted By PJmax

He's got a standard 15A breaker feeding several...

He's got a standard 15A breaker feeding several GFI receptacles.
It's the 15A breaker that's tripping.
04-21-20, 11:41 PM
Replies: 5
Views: 219
Posted By stickshift

Sounds like running another circuit would be the...

Sounds like running another circuit would be the best answer.

As Pete said, the 15 amp circuit you have must stay at 15 amps unless you replace all of the 14 ga wire or cable with 12 ga.
04-21-20, 09:51 PM
Replies: 5
Views: 219
Posted By PJmax

Unfortunately with #14 wiring you are limited to...

Unfortunately with #14 wiring you are limited to protecting it at 15A.
You cannot upgrade to a 20A breaker.
You'd need to replace it with #12 in order to increase the breaker size.