In every Power Company I've ever worked with, the...

In every Power Company I've ever worked with, the Power Company owns the overhead feed to the house including the connections at each end.
Call them and schedule an appointment to have the cable...
01-19-17, 08:05 AM
Replies: 43
Views: 2,451
Posted By Electromen

Let me try to explain the Main Neutral. I'm...

Let me try to explain the Main Neutral. I'm going to use layman's terms as much as possible.
If anyone wants to correct me or add to this, feel free.

The Main Neutral carries the unbalanced load...
01-19-17, 04:52 AM
Replies: 43
Views: 2,451
Posted By Electromen

Electer, You have an open neutral. The...

Electer, You have an open neutral.
The voltage will fluctuate, I've seen it as high as 177V
WARNING: Do not disconnect any plumbing grounds or ground rods, you could die.
Possible Causes:
1. ...