10-21-08, 03:33 PM
Replies: 14
Views: 6,258
Posted By perhaps0369

problem appears to be fixed

well i hate to post this, but in the future should anyone experience the same problem, this was my fix. after talking with thermofridge, he said it seemed like the furnace had water in the heat...
10-16-08, 12:23 PM
Replies: 14
Views: 6,258
Posted By perhaps0369

just tested the manifold pressure, book states...

just tested the manifold pressure, book states its to be within .3 of 3.5 wc. while running the pressure was about 3.3 to start and dropped to just above 3. the furnace still stopped at the 8-10...
10-11-08, 06:03 PM
Replies: 14
Views: 6,258
Posted By perhaps0369

[QUOTE=ecman51`;1444687]Gas problem? Never even...

[QUOTE=ecman51`;1444687]Gas problem? Never even thought of that, actually. Like, someone adjusted the pressure setting too high? Hmmm. Who put in this furnace anyway. Fess up. YOU did, didn't you? :D...
10-11-08, 05:30 PM
Replies: 14
Views: 6,258
Posted By perhaps0369

i don't believe there are any dampers in the...

i don't believe there are any dampers in the ducts, the plenum does get pretty hot to the touch, but i am using the old furnace as a judge. you can touch it though. would the furnace continue to not...
10-11-08, 04:21 PM
Replies: 14
Views: 6,258
Posted By perhaps0369

as for the heating ducts, there is seven heat...

as for the heating ducts, there is seven heat lines, one of which is brand new. two are not hooked up yet either. i checked the rest when the furnace does blow and there is more air now than before,...
10-11-08, 01:59 PM
Replies: 14
Views: 6,258
Posted By perhaps0369

i will do that, but so you know there is no...

i will do that, but so you know there is no return duct attached yet. this furnace is hanging from rafters, and the return is completely open, with a filter only. bottom opening is 23x20. the filter...
10-11-08, 10:26 AM
Replies: 14
Views: 6,258
Posted By perhaps0369

amana 90 won't refire and locks out

i have an amana air command 90, model number gcca090ax50, that was just installed. during testing i found that the furnace fires initially and heats for 9-10 min. it then shuts the flame off, the...