need help wiring a honeywell thermostat
#1
Member
Thread Starter
Join Date: Sep 2009
Location: Alabama
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
need help wiring a honeywell thermostat
I have a trane weathertron baystat240A thermostat for my trane heatpump. I need help wiring in a honeywell 7500D thermostat. The wires on my old thermostat are on post with the following letters:
R
T
O
G
Y
X2
B
W
Can you tell me which post to use with the new one?
R
T
O
G
Y
X2
B
W
Can you tell me which post to use with the new one?
Last edited by needhelp123; 09-18-09 at 12:13 PM.
#3
Member
Thread Starter
Join Date: Sep 2009
Location: Alabama
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
There is no Y1...is Y the Y1? and do I leave the jumper between R and RC? What was T used for on the old thermostat?
Last edited by needhelp123; 09-19-09 at 06:22 AM. Reason: left something out
#4
Leave the jumper in place.
T was outdoor sensor, if it was too cold out, it would turn on the back up heat.
#5
Member
Thread Starter
Join Date: Sep 2009
Location: Alabama
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
By the way my heat pump is a Trane XE 1000.
Last edited by needhelp123; 09-19-09 at 07:33 AM. Reason: one more thing
#6
The t-stat will kick in the Aux heat as needed if the heat pump falls behind.
If it gets below 5˚ and it can't keep you and you are seeing the Aux on the screen all the time, then switch over to Emergencey heat.
Also, for heat pump system you are best to set it and forget it. or only do 2 to 3˚ temp set back.. Not 10˚
If it gets below 5˚ and it can't keep you and you are seeing the Aux on the screen all the time, then switch over to Emergencey heat.
Also, for heat pump system you are best to set it and forget it. or only do 2 to 3˚ temp set back.. Not 10˚
#8
Member
Join Date: Sep 2009
Location: Pennsylvania
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Honeywell RTH7600
I need help interpreting the wiring to replace my existing thermostat with a Honeywell RTH7600. I have a Gibson 3 ton heat pump with Residential Thermal Storage aux/emergency heat. The connections on the old unit don't seem to match the installation manual.
Term Wire Color
W White
O Orange
Y Yellow
B Blue
G Green
R Red
X N/C
H N/C
T N/C
I know this is being beaten to death but would appreciate any advice.
Term Wire Color
W White
O Orange
Y Yellow
B Blue
G Green
R Red
X N/C
H N/C
T N/C
I know this is being beaten to death but would appreciate any advice.
Last edited by tpm1285; 09-28-09 at 11:56 AM. Reason: Add info
#10
Going back to the original poster...
You must also configure your new stat to match your system.
Option 170 = 7
190 = 0
You must also configure your new stat to match your system.
Option 170 = 7
190 = 0
Last edited by Houston204; 10-01-09 at 09:27 PM. Reason: Wrong spot
#11
http://i151.photobucket.com/albums/s...lQ674L1272.jpg
TPM, was your old stat a Honeywell with a Q674L subbase?
Looks like...
G = green
Rc & R = red
Aux & E = white
C = blue
O/B = orange
Y = yellow
Option 170 = 7
option 190 = 0
http://i151.photobucket.com/albums/s...ellRTH7600.jpg
TPM, was your old stat a Honeywell with a Q674L subbase?
Looks like...
G = green
Rc & R = red
Aux & E = white
C = blue
O/B = orange
Y = yellow
Option 170 = 7
option 190 = 0
http://i151.photobucket.com/albums/s...ellRTH7600.jpg