Changing Out Honeywell Thermostat
#1
Member
Thread Starter
Join Date: Mar 2010
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Changing Out Honeywell Thermostat
I would like to replace my old Honeywell thermostat T8411R with a new Honeywell thermostat TH8320U. I have a Trane Heat Pump Model TWNO42C and a Trane air handler TWEO42C14FCO. There are 6 wires going to the old thermostat. They go to: G,C,R,W1,O and W2. In addition, W2 and E are jumped.
OLD NEW
G
C
R
W1
O
W2
Old Jump: W2&E New Jump:
Any assistance you can provide in wiring my new thermostat and providing the correct Setup Functions would be greatly appreciated.
OLD NEW
G
C
R
W1
O
W2
Old Jump: W2&E New Jump:
Any assistance you can provide in wiring my new thermostat and providing the correct Setup Functions would be greatly appreciated.
Last edited by JonAA; 03-19-10 at 07:36 AM.
#5
Ok,
Old-----New----Air Handler------HP
G-------G---------G
C-------C---------C/B--------------C/B
R-------R/Rc-------R---------------R
W1-----Y-----------Y---------------Y
O-------O/B--------O--------------O
W2-----Aux&E-----W1/W2--------X
Jumper in Aux and E, and W1 and W2 at air handler.
Set up menu.
170-7
180-1
190-0
200-0
220-2
240 to 270-2 (Not all will show up)
280-1 (makes great night light)
300-0
340- Did you get outdoor sensor? Yes=2
if you got snesor, below setting.
350-0
360-40
Rest you can figure out, if not sure, let me know.
280-
Old-----New----Air Handler------HP
G-------G---------G
C-------C---------C/B--------------C/B
R-------R/Rc-------R---------------R
W1-----Y-----------Y---------------Y
O-------O/B--------O--------------O
W2-----Aux&E-----W1/W2--------X
Jumper in Aux and E, and W1 and W2 at air handler.
Set up menu.
170-7
180-1
190-0
200-0
220-2
240 to 270-2 (Not all will show up)
280-1 (makes great night light)
300-0
340- Did you get outdoor sensor? Yes=2
if you got snesor, below setting.
350-0
360-40
Rest you can figure out, if not sure, let me know.
280-