iaq wiring help
#1
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
iaq wiring help
Here are my components.
Goodman Furnace / GMVC950704CXa 95% AFUE 2-stage Variable Speed Gas furnace 70k btu
Goodman HP / SSZ140361a Split system heat pump 14 seer 3ton
VisionPro IAQ THM5421C / TH9421C1004
Hermidifier G-100ES Duct mount Humidifier Power flow through
My available furnace contacts are
1 2 R C G W1 W2 Y1 Y2 O DEHUM
HP contacts
R W2 O Y C
EIM Contacts
CONV HP
W1 /O-B
W2 /AUX
W3 /AUX2
Y / Y
Y2 / Y2
G / G
L ?
There is a jumper on R, RC, & RH
Is this right?
EIM----------------- furnace------------------------ HP
R-RC-RH-----------------R---------------------------R
C------------------------C---------------------------C
W1-O/B------------------O--------------------------O
W2-AUX-----------------W1 ------------------------ W2
W3-AUX-----------------W2-------------------------
Y---------------------- Y --------------------------- Y
Y2--------------------- Y2 -------------------------
G------------------------G--------------------------
Thanks in advance
Dave
Goodman Furnace / GMVC950704CXa 95% AFUE 2-stage Variable Speed Gas furnace 70k btu
Goodman HP / SSZ140361a Split system heat pump 14 seer 3ton
VisionPro IAQ THM5421C / TH9421C1004
Hermidifier G-100ES Duct mount Humidifier Power flow through
My available furnace contacts are
1 2 R C G W1 W2 Y1 Y2 O DEHUM
HP contacts
R W2 O Y C
EIM Contacts
CONV HP
W1 /O-B
W2 /AUX
W3 /AUX2
Y / Y
Y2 / Y2
G / G
L ?
There is a jumper on R, RC, & RH
Is this right?
EIM----------------- furnace------------------------ HP
R-RC-RH-----------------R---------------------------R
C------------------------C---------------------------C
W1-O/B------------------O--------------------------O
W2-AUX-----------------W1 ------------------------ W2
W3-AUX-----------------W2-------------------------
Y---------------------- Y --------------------------- Y
Y2--------------------- Y2 -------------------------
G------------------------G--------------------------
Thanks in advance
Dave
#2
Your heat pump is single stage, so Y2 is not wired up at all.
Other than that, it's wired up right.
Any questions on IAQ's installer set up?
Do you want to wire up the humidifier, and dehumidifier control on your system?
Other than that, it's wired up right.
Any questions on IAQ's installer set up?
Do you want to wire up the humidifier, and dehumidifier control on your system?
#4
On the furnace, you want Dipswitch set at.
S3
1-off
2-on
3-on
4-off
S3
5-on
6-on
You need to add a jumper from Y1 to Y2 at the furnace. Also, a jumper from Y to O at the furnace.
Dehumidifier- At the EIM Add a jumper from one of the R's to DHUM1. Then DHUM2 to DHUM at the furnace.
Humidifier- What brand is it? since you said powered unit, I'm guessing the unit has it's own low voltage transformer. If so, the two low voltage wires goes to HUM1 and HUM2. Then plug the unit into an outlet.
S3
1-off
2-on
3-on
4-off
S3
5-on
6-on
You need to add a jumper from Y1 to Y2 at the furnace. Also, a jumper from Y to O at the furnace.
Dehumidifier- At the EIM Add a jumper from one of the R's to DHUM1. Then DHUM2 to DHUM at the furnace.
Humidifier- What brand is it? since you said powered unit, I'm guessing the unit has it's own low voltage transformer. If so, the two low voltage wires goes to HUM1 and HUM2. Then plug the unit into an outlet.
#5
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
Jay you are my new hero.
The humidifier is Fedders Hermidifier G-100ES, and yes it came with its own transformer and a humidistat that I will not use.
Your instructions are as simple as they can get. It will be less for the tech to do when he comes out for final hook up @70.00 per hr. 5 kids and a mortgage I live check to chek.
I bought this setup with income tax return back in February to replace my three window units and a furnace that was at least 60 years old. I am currently replacing all of the wall stacks along exterior walls with 1" ductboard. I was told interior stacks should be fine.
Is there anything special I should need to know about the IAQ's installer set up?

The humidifier is Fedders Hermidifier G-100ES, and yes it came with its own transformer and a humidistat that I will not use.
Your instructions are as simple as they can get. It will be less for the tech to do when he comes out for final hook up @70.00 per hr. 5 kids and a mortgage I live check to chek.
I bought this setup with income tax return back in February to replace my three window units and a furnace that was at least 60 years old. I am currently replacing all of the wall stacks along exterior walls with 1" ductboard. I was told interior stacks should be fine.
Is there anything special I should need to know about the IAQ's installer set up?
#6
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
Okay you mentioned
S3
1-off
2-on
3-on
4-off
S3
5-on
6-on
On my board pic attached number 5 and 6 are under S4. Do I set these as you mentioned? I have not changed none of these yet.
[IMG]
[/IMG]
On the EIM am I able to run these wire up into the module like this or will it cause communication errors?. If I can keep them there I will shorten them up to clean up the appearance.
[IMG]
[/IMG]
S3
1-off
2-on
3-on
4-off
S3
5-on
6-on
On my board pic attached number 5 and 6 are under S4. Do I set these as you mentioned? I have not changed none of these yet.
[IMG]

On the EIM am I able to run these wire up into the module like this or will it cause communication errors?. If I can keep them there I will shorten them up to clean up the appearance.
[IMG]

#7
The humidifier is Fedders Hermidifier G-100ES, and yes it came with its own transformer and a humidistat that I will not use.
I bought this setup
Is there anything special I should need to know about the IAQ's installer set up?
160-0 (I don't advise using program mode on Heat Pump system)
172-2
173-0
174-1
176-2
180-0
190-0
200-1
210-0
220-2
240-2
250-3
280-1
345-2
346-0
350-15 (Can bring up higher if you feel you are not "warm" when it's below 15˚)
360-35
370-1
372-3
374-2
379-1
384-1
540-
On the EIM am I able to run these wire up into the module like this or will it cause communication errors?. If I can keep them there I will shorten them up to clean up the appearance.
#8
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
I am not able to find the full manual on this
Not much of a manual, guess they had to cut cost somewhere.
Is the transformer built inside the unit??
Bought the units from here Desco Energy
They are local to me 10 minutes away.
Do a Manual-J on this as well?
I guess I am anal about wire management. Now that I know that they can stay there I will clean that up even more. Like when I build a pc, wire management is key to coolness inside the tower. I hate restrictions of air flow.
#9
If the low voltage wire off of that is not "hot", then you can either get power from R or use the transformer.
Who's standing by for warranty? Goodman says on their fine print that they will not honor warranty if it was done outside of a pro install.
Manual-J is a load calc program to see what size equipment your home needs. How big and age of your home? Where are you out of?
Keep up the good job!
They are local to me 10 minutes away.
Manual-J is a load calc program to see what size equipment your home needs. How big and age of your home? Where are you out of?
I guess I am anal about wire management. Now that I know that they can stay there I will clean that up even more. Like when I build a pc, wire management is key to coolness inside the tower. I hate restrictions of air flow.
#10
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
If the low voltage wire off of that is not "hot", then you can either get power from R or use the transformer
Who's standing by for warranty? Goodman says on their fine print that they will not honor warranty if it was done outside of a pro install.
Manual-J is a load calc program to see what size equipment your home needs. How big and age of your home? Where are you out of?
On with the wire management. Now I can put the cover on with no wires showing. I have not installed the humidifier yet maybe next weekend.
[IMG]

Here is a pic of my furnace to date
[IMG]

Here is a pic of one of my trunks. Guy from Desco said he was impressed with it when he came out Thursday. He said most guys just square them off at the turns. To me that is another air restriction.
[IMG]

#11
Wire the transformer to be "always hot" or you can wire it on your 110v on the furnace.
HUM1 will go to one of the screws on the transformer.
HUM2 will go to one of the wire on the humidifier.
Other wire from Humidifier goes to the other screw on transformer.
Near the bottom of the page there more info on Desco's warranty. Desco will be coming out to do the final hookups brazing lines charging system doulble check my work and do the initial startup.
On with the wire management. Now I can put the cover on with no wires showing.
Here is a pic of my furnace to date
Here is a pic of one of my trunks. Guy from Desco said he was impressed with it when he came out Thursday. He said most guys just square them off at the turns. To me that is another air restriction.
#12
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
Thank you for the compliments now you made my head bigger than it should be.
One more question
On the evaporator there is 2 drain ports one is just slightly higher than the other. Which one is primary and should the secondary be plugged? That is one of the things I have not researched yet. Man now I am getting lazy. I forgot google was my friend.
One more question
On the evaporator there is 2 drain ports one is just slightly higher than the other. Which one is primary and should the secondary be plugged? That is one of the things I have not researched yet. Man now I am getting lazy. I forgot google was my friend.

#13
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
Never mind I found this at whirlpools site
That tells me that the one that is slightly higher is secondary and that I cannot plug it, I need to set up a drain pan for it. If water comes out of it then I know there is problems with primary drain.
The primary I will have directly connected to one of my other drain lines. I will put a small trap and breather just past the trap because it will be a lengthy run.
Connect secondary drain line connection to the drain pan
(small hole). Route the secondary drain to empty at a location
easily seen, so that any drainage coming from that line would
be noticed. If there is drainage from the secondary drain line,
a problem exists with the primary drain system, which should
be investigated and corrected.
(small hole). Route the secondary drain to empty at a location
easily seen, so that any drainage coming from that line would
be noticed. If there is drainage from the secondary drain line,
a problem exists with the primary drain system, which should
be investigated and corrected.
The primary I will have directly connected to one of my other drain lines. I will put a small trap and breather just past the trap because it will be a lengthy run.
#14
Looked at your photo, I don't see the drain port or the lineset on front of the case?
For homes with basements, I never bother with the 2nd drain, just in the attic or places you don't see the unit itself.
A trap is not needed on gas furnace set up, just on air handler or roof top system. (gas set up, drain is under pressure, where other it's under negative)
When the drain makes the turn down put in a "T" and just put on a cap (don't glue) on top of the "T".
For homes with basements, I never bother with the 2nd drain, just in the attic or places you don't see the unit itself.
A trap is not needed on gas furnace set up, just on air handler or roof top system. (gas set up, drain is under pressure, where other it's under negative)
When the drain makes the turn down put in a "T" and just put on a cap (don't glue) on top of the "T".
#15
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
See, now that even made more sense to me. (all of it) Sorry about the pic the drains were on the other side. (low side) I have about 1/8% fall forward and left for drainage of condensate.
Thanks again Jay
Thanks again Jay
#17
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
Have a safe trip.
They have me working out town this week, but I will taking my laptop with so I can still get on at the motel.
Thanks again for all the help. I will report back when I have it up and running. Probably sometime time next month.
Dave
They have me working out town this week, but I will taking my laptop with so I can still get on at the motel.
Thanks again for all the help. I will report back when I have it up and running. Probably sometime time next month.
Dave
#18
Member
Thread Starter
Join Date: Jul 2010
Location: usa
Posts: 11
Received 0 Votes
on
0 Posts
I guess I lied when I said I would report back in a month. Well anyway I did have it running the next month. After initial estimates of 4500 to 5500$ I went to Jeremy at Desco said something to him about the prices. He told me to do all I can do and he would come out and give me an estimate himself stating he should be able to get it down to 2000 to 2500$. Any way he came and was surprised and said he would just charge me hourly since everything was done.
I ran all the 110, 220, and low voltage wires. The heat pump was approximately 15' from the furnace and I ran 1" electrical conduit underground to carry the 220volt @8 guage on 30amp breaker inside with disconnect at the pump and low voltage wires and a 4" electrical conduit underground to carry the line set. At the end I poured a 5'x5'x4" concrete pad around the conduits. The only thing left was to braze lines evacuate and charge then flip the breakers.
Till it was done I had a $350 initial start up bill. That is a big difference from the thousands I was fearing. There was only 1 snag, he could not get the the pump to change over to heat. The problem was if I remember was the Y to O jumper. Once that was cut we had heat.
Attached is a pic of the heat pump. Camera was having problems focusing at 1:30 in the morning.
Thanks again for the help Jay.
Dave
[IMG]
[/IMG]
I ran all the 110, 220, and low voltage wires. The heat pump was approximately 15' from the furnace and I ran 1" electrical conduit underground to carry the 220volt @8 guage on 30amp breaker inside with disconnect at the pump and low voltage wires and a 4" electrical conduit underground to carry the line set. At the end I poured a 5'x5'x4" concrete pad around the conduits. The only thing left was to braze lines evacuate and charge then flip the breakers.
Till it was done I had a $350 initial start up bill. That is a big difference from the thousands I was fearing. There was only 1 snag, he could not get the the pump to change over to heat. The problem was if I remember was the Y to O jumper. Once that was cut we had heat.
Attached is a pic of the heat pump. Camera was having problems focusing at 1:30 in the morning.
Thanks again for the help Jay.

Dave
[IMG]