Stat = Trane----TCONT602A 2H/2C
Dip Switches:
Sw1(staging delay)= 1=off
2=off
Sw2(heat off delay)= 1=on
2=on
Sw3
1=off
2=off
3=off
4=off
5=on
6=off
7=off
8=on
Thanks
Dip Switches:
2=off
2=on
Sw3
1=off
2=off
3=off
4=off
5=on
6=off
7=off
8=on
Where are you out of? Pretty large units for a new home.
Ok, These are the setting you should be at.
Sw3
1=on
2=off
3=off
4=off
5=on
6=om
7=off
8=on
T-stat hook up.
T-stat-----Fur-----A/C
Y1---------Ylo------Y1
Y2--------Y2/Y-----Y2
B----------B/C-----B/C
W---------W1
W2--------W2
G-----------G
Jumper wire at the furnace between O and Ylo
t-stat Installer Setup
1-6
3-0
5-2
6-3
9-2
10-3
31-1
Sw3
1=on
2=off
3=off
4=off
5=on
6=om
7=off
8=on
T-stat hook up.
W---------W1
W2--------W2
G-----------G
1-6
3-0
5-2
6-3
9-2
10-3
31-1
The jumper is giving the blower the correct "profile" speed in the enhanced mode.
Wonder if the dealer has done a Manual-J (Load Calc) on the home??? Your home might off been able to get by with a 80k furnace with 2 or maybe 3 ton A/C. Right now you got 120k and 4 tons.