How to change installer functions on Honeywell Prestige HD?
I have just installed a Honeywell Prestige HD, and all is fine except that I need to change the setting on installer function 190, "Reversing valve". Should take me 1 minute, right? 2 hours later, I am posting here in desperation. How do I change this setting? In the installer menu there are lots of settings, but no numbers, and no setting called "Reversing valve". Supposedly you can update settings via USB - is that the only way to change this setting? I tried it, but there is nothing in the install guide about how to do it, and all the things I tried failed. All help greatly appreciated.
#3
Member
Thread Starter
Join Date: Jul 2010
Location: US
Posts: 5
Received 0 Votes
on
0 Posts
Thanks for taking the time to reply - I appreciate it! I know I need to set it to O. Currently it is set to B. My question is not what to set it to, my question is how do I set it to O? What do I have do in order to change the value of #190 from B to O? What do I press on the keypad to do this?
#4
Banned. Rule And/Or Policy Violation
Join Date: Jul 2010
Location: US
Posts: 136
Received 0 Votes
on
0 Posts
Thanks for taking the time to reply - I appreciate it! I know I need to set it to O. Currently it is set to B. My question is not what to set it to, my question is how do I set it to O? What do I have do in order to change the value of #190 from B to O? What do I press on the keypad to do this?
#5
Member
Thread Starter
Join Date: Jul 2010
Location: US
Posts: 5
Received 0 Votes
on
0 Posts
That page tells me how to get into the installer menu (works - no problem). It then says I should use "CREATE SETUP" or "VIEW/EDIT CURRENT SETUP". I've done both of those - neither provides any option to enter a numeric setting, and neither provides a setting with a name resembling "Reversing valve".
So - how do I change setting #190 "Reversing valve"?
So - how do I change setting #190 "Reversing valve"?
#6
Member
Thread Starter
Join Date: Jul 2010
Location: US
Posts: 5
Received 0 Votes
on
0 Posts
Found it! I had to change the system type from "Conventional" to "Heat pump" - then the setting appeared! And now AC seems to work.
I now need to verify if heating works, and I am a bit confused. My old thermostat had an O wire and a W2 wire. None of the wiring examples in the install guide match that - none of them indicate use of the W2 wire. Should it be connected to AUX?
I have a Carrier FC4CNF060.
I now need to verify if heating works, and I am a bit confused. My old thermostat had an O wire and a W2 wire. None of the wiring examples in the install guide match that - none of them indicate use of the W2 wire. Should it be connected to AUX?
I have a Carrier FC4CNF060.
#7
Banned. Rule And/Or Policy Violation
Join Date: Jul 2010
Location: US
Posts: 136
Received 0 Votes
on
0 Posts
Found it! I had to change the system type from "Conventional" to "Heat pump" - then the setting appeared! And now AC seems to work.
I now need to verify if heating works, and I am a bit confused. My old thermostat had an O wire and a W2 wire. None of the wiring examples in the install guide match that - none of them indicate use of the W2 wire. Should it be connected to AUX?
I have a Carrier FC4CNF060.
I now need to verify if heating works, and I am a bit confused. My old thermostat had an O wire and a W2 wire. None of the wiring examples in the install guide match that - none of them indicate use of the W2 wire. Should it be connected to AUX?
I have a Carrier FC4CNF060.
#8
Member
Thread Starter
Join Date: Jul 2010
Location: US
Posts: 5
Received 0 Votes
on
0 Posts
THANK YOU SIR FOR YOUR HELP! Really appreciate it. Turns out I have a 2H/1C Heat Pump, and it was wired correctly. Now that I changed the system mode from Conventional to Heat Pump, everything appears to be working perfectly. THANK YOU!