IAQ 9000/Lennox/TrueSteam wiring ....

Reply

  #1  
Old 08-12-10, 09:29 AM
B
Member
Thread Starter
Join Date: Aug 2010
Location: Canada
Posts: 39
Received 0 Votes on 0 Posts
IAQ 9000/Lennox/TrueSteam wiring ....

I need to replace a White-Rodgers tstat (1F82-261) with a VisionPro 9000/EIM and add a TrueSteam humidifier. There are 7 wires in the wall (at tstat).
I believe I have the humidifier wired correctly to the EIM but am at a bit of a loss in hooking the EIM to the air handler system (Lennox CBX32M-018/024,with electric heat/1 breaker; heat pump Lennox 13HPX-024-230-11).
There are 2 multi wire cables (brown casing) entering the air handler - I assume 1 is from the heat pump and the other from the tstat ... how can identify which is which? Once I identify the cable going to the tstat, can I use 3 of those wires (out of 7) to hook up the IAQ on the wall?
I read somewhere here, that the EIM can be considered to be the tstat in this new configuration ... ?

Thank you in advance for any help you are able to pass along!
Bob
 
  #2  
Old 08-12-10, 06:02 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by bobcanuck View Post
with electric heat/1 breaker;
What's the model # on the heat bank/strip?

I assume 1 is from the heat pump and the other from the tstat ...
Correct.

how can identify which is which?
Trace it from the air handler, one would go outside to the HP, and other going towards the t-stat on the wall.

Once I identify the cable going to the tstat, can I use 3 of those wires (out of 7) to hook up the IAQ on the wall?
Yes. 1-red, 2-white, 3-blue.

I read somewhere here, that the EIM can be considered to be the tstat in this new configuration ... ?
It's a control board to run everything.

I'll wait till you get back to me on the heat strp. Unless you know W1-W2-W3 was wired up at the air handler?
 
  #3  
Old 08-13-10, 10:16 AM
B
Member
Thread Starter
Join Date: Aug 2010
Location: Canada
Posts: 39
Received 0 Votes on 0 Posts
Jay - you are a very patient person, and for that I am thankful!! The heater bank model is EB29 ... I've wired in the humidifier and can deal with the 3 wires to/from the thermostat. I am just very uncertain about the connections between the EIM and the air handler (paranoid, I guess!). Once again, thank you for your understanding!
Bob
 
  #4  
Old 08-13-10, 12:55 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by bobcanuck View Post
The heater bank model is EB29
The # is way too short.. Ones I'm seeing in the manual is ECB29-xxx

If we need to get thing going. we can leave the heat wires off for now.


EIM-----AH-------HP
R's-------R--------R
G--------G
Y------------------Y1
O------------------O
C--------C---------C

We'll come back for the Aux hook up once we get the full mode # on the bank.
 
  #5  
Old 08-13-10, 03:44 PM
B
Member
Thread Starter
Join Date: Aug 2010
Location: Canada
Posts: 39
Received 0 Votes on 0 Posts
The info I found on a sticker outside the AH, for the heater is as follows ....

ECB29 - 2.5, 5, 6 - 2P
ECB29 - 5CB, 6CB - 2P

On a tag inside the AH ECB29 - 5CB-2P
It is a very basic, condo contractor installed system, as you can see.

Thank you for the wiring info you've sent me already ... are all connections to be made at TB-1 inside the AH?
Regards,
Bob
 
  #6  
Old 08-13-10, 03:48 PM
B
Member
Thread Starter
Join Date: Aug 2010
Location: Canada
Posts: 39
Received 0 Votes on 0 Posts
Did you receive my original reply? (system prob?)
ECB29 - 5CB - 2P
 
  #7  
Old 08-13-10, 04:31 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by bobcanuck View Post
On a tag inside the AH ECB29 - 5CB-2P
Ok, you have a single stage heat strip.

So, Aux1----W1--W1 at HP

connections to be made at TB-1 inside the AH?
Yes.

Sorry not getting back to you right away, been having bad storms here this afternoon, and now heading out of town for the evenig.
 
  #8  
Old 08-14-10, 08:50 AM
B
Member
Thread Starter
Join Date: Aug 2010
Location: Canada
Posts: 39
Received 0 Votes on 0 Posts
Thank you Jay ... I will tackle the wiring on Monday and let you know the outcome.
 
  #9  
Old 08-14-10, 11:45 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Ok, here is the recap.

EIM-----AH-------HP
R's-------R--------R
G--------G
Y------------------Y1
O------------------O
C--------C---------C
Aux1---W1-------W1

Advance setting on IAQ. Anything with "E" must be set to a number value.

110 to 150 you can figure out, ask if not sure.
160-0 (On heat pump system. is best to set it and forget it.)
172-2
173-0
174-1
176-1
180-1
190-0
200-0
210-0
220-2
240-3
280-0
300- up to you.
340-0
342- Did you get an outdoor sensor? If yes-1
345-2
346-0
347-2
350-20
360-35
370-1
372-3
374-0
379-1
383-3
384-0
386-0


Ask if you have questions on rest of the settings.
 
  #10  
Old 08-19-10, 01:21 PM
B
Member
Thread Starter
Join Date: Aug 2010
Location: Canada
Posts: 39
Received 0 Votes on 0 Posts
Jay ... I finally got up the nerve today and wired the system as you had instructed - everything seems to be working properly !!! Thank you !
One final question, however, you suggested I set parameter 0379 to 1 (dehumidify with A/C) ... do I need additional wiring (AH, HP, EIM) for this function?
Best regards,
Bob
 
  #11  
Old 08-19-10, 01:40 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by bobcanuck View Post
Jay ... I finally got up the nerve today and wired the system as you had instructed - everything seems to be working properly !!! Thank you !
Thanks for the update, and glad to hear it's all working.

One final question, however, you suggested I set parameter 0379 to 1 (dehumidify with A/C) ... do I need additional wiring (AH, HP, EIM) for this function?
Nope. If you set the "DHUM" to 45%, and if the home becomes above 50% (5% above set point), it will force the A/C on and try to bring down the humidity in the home below 50%. If the humidity is very high, it may "over cool" the home up to 3˚ below set point.
 
  #12  
Old 08-19-10, 02:47 PM
B
Member
Thread Starter
Join Date: Aug 2010
Location: Canada
Posts: 39
Received 0 Votes on 0 Posts
Once again, thanks Jay - your assistance has been invaluable!
 
 