IAQ 9000/Lennox/TrueSteam wiring ....
#1
Member
Thread Starter
IAQ 9000/Lennox/TrueSteam wiring ....
I need to replace a White-Rodgers tstat (1F82-261) with a VisionPro 9000/EIM and add a TrueSteam humidifier. There are 7 wires in the wall (at tstat).
I believe I have the humidifier wired correctly to the EIM but am at a bit of a loss in hooking the EIM to the air handler system (Lennox CBX32M-018/024,with electric heat/1 breaker; heat pump Lennox 13HPX-024-230-11).
There are 2 multi wire cables (brown casing) entering the air handler - I assume 1 is from the heat pump and the other from the tstat ... how can identify which is which? Once I identify the cable going to the tstat, can I use 3 of those wires (out of 7) to hook up the IAQ on the wall?
I read somewhere here, that the EIM can be considered to be the tstat in this new configuration ... ?
Thank you in advance for any help you are able to pass along!
Bob
I believe I have the humidifier wired correctly to the EIM but am at a bit of a loss in hooking the EIM to the air handler system (Lennox CBX32M-018/024,with electric heat/1 breaker; heat pump Lennox 13HPX-024-230-11).
There are 2 multi wire cables (brown casing) entering the air handler - I assume 1 is from the heat pump and the other from the tstat ... how can identify which is which? Once I identify the cable going to the tstat, can I use 3 of those wires (out of 7) to hook up the IAQ on the wall?
I read somewhere here, that the EIM can be considered to be the tstat in this new configuration ... ?
Thank you in advance for any help you are able to pass along!
Bob
#2
What's the model # on the heat bank/strip?
Correct.
Trace it from the air handler, one would go outside to the HP, and other going towards the t-stat on the wall.
Yes. 1-red, 2-white, 3-blue.
It's a control board to run everything.
I'll wait till you get back to me on the heat strp. Unless you know W1-W2-W3 was wired up at the air handler?
I assume 1 is from the heat pump and the other from the tstat ...
how can identify which is which?
Once I identify the cable going to the tstat, can I use 3 of those wires (out of 7) to hook up the IAQ on the wall?
I read somewhere here, that the EIM can be considered to be the tstat in this new configuration ... ?
I'll wait till you get back to me on the heat strp. Unless you know W1-W2-W3 was wired up at the air handler?
#3
Member
Thread Starter
Jay - you are a very patient person, and for that I am thankful!! The heater bank model is EB29 ... I've wired in the humidifier and can deal with the 3 wires to/from the thermostat. I am just very uncertain about the connections between the EIM and the air handler (paranoid, I guess!). Once again, thank you for your understanding!
Bob
Bob
#4
The # is way too short.. Ones I'm seeing in the manual is ECB29-xxx
If we need to get thing going. we can leave the heat wires off for now.
EIM-----AH-------HP
R's-------R--------R
G--------G
Y------------------Y1
O------------------O
C--------C---------C
We'll come back for the Aux hook up once we get the full mode # on the bank.
If we need to get thing going. we can leave the heat wires off for now.
EIM-----AH-------HP
R's-------R--------R
G--------G
Y------------------Y1
O------------------O
C--------C---------C
We'll come back for the Aux hook up once we get the full mode # on the bank.
#5
Member
Thread Starter
The info I found on a sticker outside the AH, for the heater is as follows ....
ECB29 - 2.5, 5, 6 - 2P
ECB29 - 5CB, 6CB - 2P
On a tag inside the AH ECB29 - 5CB-2P
It is a very basic, condo contractor installed system, as you can see.
Thank you for the wiring info you've sent me already ... are all connections to be made at TB-1 inside the AH?
Regards,
Bob
ECB29 - 2.5, 5, 6 - 2P
ECB29 - 5CB, 6CB - 2P
On a tag inside the AH ECB29 - 5CB-2P
It is a very basic, condo contractor installed system, as you can see.
Thank you for the wiring info you've sent me already ... are all connections to be made at TB-1 inside the AH?
Regards,
Bob
#7
Ok, you have a single stage heat strip.
So, Aux1----W1--W1 at HP
Yes.
Sorry not getting back to you right away, been having bad storms here this afternoon, and now heading out of town for the evenig.
So, Aux1----W1--W1 at HP
connections to be made at TB-1 inside the AH?
Sorry not getting back to you right away, been having bad storms here this afternoon, and now heading out of town for the evenig.
#9
Ok, here is the recap.
EIM-----AH-------HP
R's-------R--------R
G--------G
Y------------------Y1
O------------------O
C--------C---------C
Aux1---W1-------W1
Advance setting on IAQ. Anything with "E" must be set to a number value.
110 to 150 you can figure out, ask if not sure.
160-0 (On heat pump system. is best to set it and forget it.)
172-2
173-0
174-1
176-1
180-1
190-0
200-0
210-0
220-2
240-3
280-0
300- up to you.
340-0
342- Did you get an outdoor sensor? If yes-1
345-2
346-0
347-2
350-20
360-35
370-1
372-3
374-0
379-1
383-3
384-0
386-0
Ask if you have questions on rest of the settings.
EIM-----AH-------HP
R's-------R--------R
G--------G
Y------------------Y1
O------------------O
C--------C---------C
Aux1---W1-------W1
Advance setting on IAQ. Anything with "E" must be set to a number value.
110 to 150 you can figure out, ask if not sure.
160-0 (On heat pump system. is best to set it and forget it.)
172-2
173-0
174-1
176-1
180-1
190-0
200-0
210-0
220-2
240-3
280-0
300- up to you.
340-0
342- Did you get an outdoor sensor? If yes-1
345-2
346-0
347-2
350-20
360-35
370-1
372-3
374-0
379-1
383-3
384-0
386-0
Ask if you have questions on rest of the settings.
#10
Member
Thread Starter
Jay ... I finally got up the nerve today and wired the system as you had instructed - everything seems to be working properly !!! Thank you !
One final question, however, you suggested I set parameter 0379 to 1 (dehumidify with A/C) ... do I need additional wiring (AH, HP, EIM) for this function?
Best regards,
Bob
One final question, however, you suggested I set parameter 0379 to 1 (dehumidify with A/C) ... do I need additional wiring (AH, HP, EIM) for this function?
Best regards,
Bob
#11
One final question, however, you suggested I set parameter 0379 to 1 (dehumidify with A/C) ... do I need additional wiring (AH, HP, EIM) for this function?