I have a totaline thermostat that just went blank. I checked the circuits and all were on. I reset them anyway but still blank. I took the thermostate cover off the wall and tried it on another floor and it worked, so I don't think it's the thermostat. From reading the forum it seems it's either a blown transformer or a blown fuse. I don't know where the fuse would be or how to determine if the transformer is bad. Any info on this would be very helpful and appreciative. Thanks.
#2
Do you have a meter?
Take a reading between R and C, should be about 24 volts.
What it the make and model of the furnace? The fuse most of the time is on the board of the newer equipement.
Take a reading between R and C, should be about 24 volts.
What it the make and model of the furnace? The fuse most of the time is on the board of the newer equipement.