Honeywell VisionPRO8000 TH8320U1008 Hookup

Howdy y'all. First post.

As the title indicates I have a question about installing the TH8320 thermostat from Honeywell. A little background info first:

My A/C-Heating system is an A/C heatpump system from Ruud/Rheem. For the heat it is single stage electric. It also has an electric coil that provides for emergency heat.

My previous thermostat is an older model Honeywell digital/programmable thermostat. That thermostat is a CT3611R4443 model. It was hooked up as follows:

B < blue wire
C < brown wire
R < red wire
Y/W1 < yellow wire * Y and W1 are jumpered together
G < green wire
W2 < white wire
L < no connection
E < no connection
O < no connection

For the new VisionPRO thermostat this is how I think it needs to be connected:

O/B < blue wire
C < brown wire
R < red wire * R and RC should be jumpered together
Y < yellow wire
G < green wire
AUX < white wire * AUX and E should be jumpered together

Is this the correct wiring? Also, for program setting 0190 for the heat/cool valve should the setting be 0 or 1?

Many thanks in advance.
 

Last edited by SyberTiger; 08-13-10 at 05:15 PM.
  #2  
Old 08-13-10, 04:53 PM
S
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
ADDITIONAL INFO:

My outside unit is a 3 1/2 ton Ruud with model number RPKA043JA2. The inside air handler unit is also Ruud with model number UHQA-1608BNV. There are 6 total wires as previously specified going to the thermostat.
 

Last edited by SyberTiger; 08-13-10 at 05:18 PM.
  #3  
Old 08-13-10, 09:18 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Your wiring is correct, and option 190 = 1.
 
  #4  
Old 08-14-10, 03:27 PM
S
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Thank you Houston204 for your reply. I was curious as to where in my heatpump manual would I find the information that would have told me that option 190 should be set to 1?

Is there a certain section in the manual or a spec in there to look at? Just curious. Maybe you just knew what the setting should be based on your past experience with Ruud heatpumps.

Thanks again.
 
  #5  
Old 08-15-10, 12:01 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
The O/B terminal controls your reversing valve.
O = energized for cooling.
B = energized for heating.
You posted that you were not using the O terminal, so configure the O/B terminal to be B (energized for heating.)

(I also knew that Rheem and Ruud energize the reversing valve to heat.)

 
  #6  
Old 08-15-10, 08:15 PM
S
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Originally Posted by Houston204
The O/B terminal controls your reversing valve.
O = energized for cooling.
B = energized for heating.
Ahhhh, I get it. I didn't understand this little tidbit until you posted that little jewel of info. Thanks again!
 
 