Trying to wire IAQ to Burnham RSM/96 oil boiler.
I got a vision pro IAQ because I wanted to have the heat pump lockout and switch the the boiler automatically. I think I got the heat pump wired correct (Trane XL15I / 4TEE3F31B1000A Air Handler). I have tried hooking up the furnace but I don't think I did it right. It is a Burnham RSM/96 boiler (2 zones) with domestic hot water.
The heat pump has a 24 volt source and so does the boiler. When I try to hook up the boiler's 24 volt wires the heat pump "cools" with heat. so right now I have all the jumpers between R/Rc/Rh connected.
I replaced the "old thermostat" with the IAQ in the diagram below. I thought a drawing of boiler's 24 volt wiring would be better then a photo in this case.

TIA
The heat pump has a 24 volt source and so does the boiler. When I try to hook up the boiler's 24 volt wires the heat pump "cools" with heat. so right now I have all the jumpers between R/Rc/Rh connected.
I replaced the "old thermostat" with the IAQ in the diagram below. I thought a drawing of boiler's 24 volt wiring would be better then a photo in this case.

TIA
#2
What area is the HP heating/cooling? I take it the other zone will be heating while the HP does the other?
Where or what area are you using the boiler for?
The stat you are planing on taking out was the HP tied to this before?
Where or what area are you using the boiler for?
The stat you are planing on taking out was the HP tied to this before?
#3
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 9
Received 0 Votes
on
0 Posts
Where or what area are you using the boiler for?
1 zone is the 3 bedrooms ( which I will leave untouched or might just tie both zones together if the wife isn't happy We like a cool bedroom.)
The other zone is for the rest of the house which is the thermostat I what to replace.
The stat you are planing on taking out was the HP tied to this before?
#5
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 9
Received 0 Votes
on
0 Posts
Yes it has an electric coil in it. Not sure the size off hand.
#6
Ok, this is going to be a bit tricky.
If we wire this up, there's few things can be done.
1- If we wire the boiler to the EIM control, your air handler back up heat will not come on, it will turn on the boiler if the temps falls behind and lock out. The coil will only come on when the system goes into a defrost.
2- Add a relay/switch to switch between the coil and boiler. You'll have to switch the switch over to one of the two you want working.
3- Wire boiler with a relay, and coil to the EIM.. Stage one will be the coil. stage 2 will be the boiler. Down fall is the air handler will be running when the system goes into a lock out.
I am going to ask another member here to see if he can give us some feedback/ideal since I've never had to do this type of set up.
If we wire this up, there's few things can be done.
1- If we wire the boiler to the EIM control, your air handler back up heat will not come on, it will turn on the boiler if the temps falls behind and lock out. The coil will only come on when the system goes into a defrost.
2- Add a relay/switch to switch between the coil and boiler. You'll have to switch the switch over to one of the two you want working.
3- Wire boiler with a relay, and coil to the EIM.. Stage one will be the coil. stage 2 will be the boiler. Down fall is the air handler will be running when the system goes into a lock out.
I am going to ask another member here to see if he can give us some feedback/ideal since I've never had to do this type of set up.
#7
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 9
Received 0 Votes
on
0 Posts
Ok, this is going to be a bit tricky.
If we wire this up, there's few things can be done.
1- If we wire the boiler to the EIM control, your air handler back up heat will not come on, it will turn on the boiler if the temps falls behind and lock out. The coil will only come on when the system goes into a defrost.
2- Add a relay/switch to switch between the coil and boiler. You'll have to switch the switch over to one of the two you want working.
3- Wire boiler with a relay, and coil to the EIM.. Stage one will be the coil. stage 2 will be the boiler. Down fall is the air handler will be running when the system goes into a lock out.
I am going to ask another member here to see if he can give us some feedback/ideal since I've never had to do this type of set up.
If we wire this up, there's few things can be done.
1- If we wire the boiler to the EIM control, your air handler back up heat will not come on, it will turn on the boiler if the temps falls behind and lock out. The coil will only come on when the system goes into a defrost.
2- Add a relay/switch to switch between the coil and boiler. You'll have to switch the switch over to one of the two you want working.
3- Wire boiler with a relay, and coil to the EIM.. Stage one will be the coil. stage 2 will be the boiler. Down fall is the air handler will be running when the system goes into a lock out.
I am going to ask another member here to see if he can give us some feedback/ideal since I've never had to do this type of set up.
Thanks for your help!! I didn't mean for this to be so difficult. I thought this thermostat would work without much issue.