Evcon 3600-367P to Honeywell RTH7500D

I have a heat pump with electric emergency heat.

On the Evcon thermostat, I have:

O - White
R - Red
G - Green
Y - Yellow
W2 - White
X - Blue

There is no X on the Honeywell. Where should I hook the blue wire?

Thanks
 
  #2  
Old 08-27-10, 07:53 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Welcome aboard.

X is "common", you can use that on C.

Here is how the wires will match.

Old----------New
O - White---O/B
R - Red------R/Rc
G - Green---G
Y - Yellow---Y
W2 - White--Aux w/ jumper to E
X - Blue-----C

System set up menu.

170-7
180-1
190-0
240-3 (If it shows up.)
270-3

Let me know if you have questions on the rest of the settings.
 
  #3  
Old 08-27-10, 08:30 PM
M
Member
Thread Starter
Join Date: Aug 2010
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Thanks Jay.

Two things

1. Should R go to R or RC (the Honeywell has both)

2. What do you mean by jumper (W2 - White--Aux w/ jumper to E)? I assume you mean wire Aux and E together? What gauge wire should I use for this?

Thanks
 
  #4  
Old 08-27-10, 09:15 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by mpriley02 View Post
1. Should R go to R or RC (the Honeywell has both)
It don't matter.. Either one since there is a jumper wire in place.

2. What do you mean by jumper (W2 - White--Aux w/ jumper to E)? I assume you mean wire Aux and E together? What gauge wire should I use for this?
You can use a small piece of t-stat wire between Aux and E, and white can land on either one of those two slot.
 
 