replacing lennox thermostatic base plate (Q674L-1355) with a RTH7600
#1
Member
Thread Starter
Join Date: Sep 2010
Location: canada
Posts: 2
Received 0 Votes
on
0 Posts

well after lots of research i could not find the info.
So i called honeywell at 1-800-468-1502 but they were close.
So i called them the next day, was on hold for 20 minutes for them to
find out the info for me.
here is the info.
I used the base plate # as there are several thermostats that used the same base plate.
here is the wireing info
old unit new unit
R goes to O/B
Y goes to E
M goes to Y
X goes to C
F goes to G
V goes to R or Rc ( there is a jumper there leave it )
L goes to L
A IS NOT USED ANY MORE
---------------------------------------------
on the old Thermostat
Vr was jumpered to V
E was not hooked up
---------------------------------------------
after installation
function 0170 was set to #7
function 0190 was set to #0
function 0270 was set to #9
hope this helps every one
thanks
Vistec
So i called honeywell at 1-800-468-1502 but they were close.
So i called them the next day, was on hold for 20 minutes for them to
find out the info for me.
here is the info.
I used the base plate # as there are several thermostats that used the same base plate.
here is the wireing info
old unit new unit
R goes to O/B
Y goes to E
M goes to Y
X goes to C
F goes to G
V goes to R or Rc ( there is a jumper there leave it )
L goes to L
A IS NOT USED ANY MORE
---------------------------------------------
on the old Thermostat
Vr was jumpered to V
E was not hooked up
---------------------------------------------
after installation
function 0170 was set to #7
function 0190 was set to #0
function 0270 was set to #9
hope this helps every one
thanks
Vistec
#2
Member
Thread Starter
Join Date: Sep 2010
Location: canada
Posts: 2
Received 0 Votes
on
0 Posts
replacing lennox thermostatic base plate (Q674L-1355) with a RTH7600
It seems honey well forgot one step
they just call me to inform me
i need to also put a jumper from E on the new unit to AUX
if not the aux heaters will not turn on
but every thing will still work
just will take longer to heat up the place
they just call me to inform me
i need to also put a jumper from E on the new unit to AUX
if not the aux heaters will not turn on
but every thing will still work
just will take longer to heat up the place