Trane XL16i, Variable Speed AH, and TCont803

Hello,

I recently had a new Trane XL16i (4ttx6048c), a Trane Variable Speed Air Handler (4tee3f49c), with 10kw electric heat, and a Trane Tcont803 thermostat installed in my house in South Florida. I am trying to confirm the wiring and thermostat settings to ensure that it is running as designed and specified.

Question 1:
The XL16i is a 2 Stage condenser unit with (1) two-step scroll compressor?

Question 2:
Based on the Tcont803 installers manual (see link below) the unit should be wired according to Fig. 8. Typical hookup of two-stage indoor and
two-step scroll cooling unit in a single transformer
system (2H/2C or 2H/1C or 1H/2C). Am I correct in this assumption?
Removed Link. Installer Guide should have been left with your system Manuals.

http://www.airconditioner-parts.com/...tallation .pdf

Wired as shown below:

T - AH - CU
Y2 - BK - Y2
W2 - W2
S1
S2
RC
R - R
W1
Y - Y - Y1
G - G
B

RC jumper to R on thermostat (factory)
R jumper to BK on air handler removed
R jumper to O on air handler


3. Which setting should be chosen in the System Type Selection in the Installer Setup Menu of the Tcont803 thermostat?

Thank you for your help. I just want the system to work as advertised considering the amount of money I paid for it.
 

Last edited by adoyle1; 11-02-10 at 12:20 PM.
  #2  
Old 11-02-10, 03:02 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by adoyle1 View Post
Question 1:
The XL16i is a 2 Stage condenser unit with (1) two-step scroll compressor?
Correct.

Question 2:
Based on the Tcont803 installers manual (see link below) the unit should be wired according to Fig. 8. Typical hookup of two-stage indoor and two-step scroll cooling unit in a single transformer system (2H/2C or 2H/1C or 1H/2C). Am I correct in this assumption?
Correct.

Wired as shown below:
Need to make a change. Otherwise, rest is correct.

W1 from t-stat goes to W1 on the air handler.

Do you have an extra wire in the wall for B?

Is B/C hooked up to C at the unit outside?

3. Which setting should be chosen in the Installer Setup Menu of the Tcont803 thermostat?
170-10
180-0
220-2
230-3
240-3
280-1 (makes a good night light if B is hooked up.)

If you have questions on the other settings, let me know.
 
  #3  
Old 11-02-10, 04:17 PM
A
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Jay, thanks for the quick response.

I only have 5 wires from the AH to the Thermostat which are all occupied. What does W1 to W1 do? Should I run this wire?

Also there are only 2 wires coming from the outside unit. I opened it and only saw two.

Why does Trane 0170-10 say "1 heat/2 cool oil furnace or 0H/2C"? The "oil furnace" makes it confusing .
 
  #4  
Old 11-02-10, 05:45 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by adoyle1 View Post
Jay, thanks for the quick response.
No problem. Glad to help.


I only have 5 wires from the AH to the Thermostat which are all occupied.
Ok, we won't be able to hook up B (Common wire) for our back light #280 setting, so leave that at 0. I suggest to put in fresh battery once a year in the t-stat.

What does W1 to W1 do? Should I run this wire?
W1 is your heat (1st stage) and you don't have two stage (W2), so W2 needs to be moved over to W1 at both t-stat and air handler. Other wise if that was left on W2, you would not have heat if the t-stat was set up 1Heat.

Also there are only 2 wires coming from the outside unit. I opened it and only saw two.
What!? You need 3 wires.. Y1 to Y, Y2 to BK, and B to B/C

Why does Trane 0170-10 say "1 heat/2 cool oil furnace or 0H/2C"? The "oil furnace" makes it confusing .
Not sure? I'm sure it was a misprint.

Do you want me to review the dip switch settings on the air handler for you?
 
  #5  
Old 11-02-10, 09:23 PM
A
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
My mistake on the original post, W1 from the Tstat goes to W1 on the AH and has a jumper to W2 on the AH.

That is correct, as it is now the T - AH - CU is as follows: Y1 - Y - Yellow/Black , and Y2 - BK - Yellow/Red. There is no third wire. I opened the condenser unit outside, and there is no wire (blue or any other color) that is not terminated, loose, or clipped. There is a blue/black wire the same gauge as the other communication wires that goes from a relay timer, through what looks like a large resistor, then into the contactor. Thoughts?

My dip switches are set as follows:

1 - ON
2- OFF
(it is a 4 ton unit)
3- OFF
4- OFF
(normal)
5- ON
6 - ON
(enhanced)
7 - ON
8 - OFF
(med-high)


Thanks Again!
 
  #6  
Old 11-02-10, 10:33 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by adoyle1 View Post
That is correct, as it is now the T - AH - CU is as follows: Y1 - Y - Yellow/Black , and Y2 - BK - Yellow/Red. There is no third wire. I opened the condenser unit outside, and there is no wire (blue or any other color) that is not terminated, loose, or clipped. There is a blue/black wire the same gauge as the other communication wires that goes from a relay timer, through what looks like a large resistor, then into the contactor.
You have the CmfortLink II System only two wire control connection. If the system is working, then I won't worry about it.

My dip switches are set as follows:
7 - ON
8 - OFF
(med-high)
You are moving too much air, won't feel "warm" with this.. The manual calls for 700 cfm on your heat coil.

Change
8 - ON
 
  #7  
Old 11-03-10, 06:50 AM
A
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
Its not a ComfortLink II, i just verified the model number. I just checked again, in daylight. It does indeed have a blue wire. The installer took it to ground on the outside unit. What does the blue wire do? Should I have the installer come back and correctly wire it?
 
  #8  
Old 11-03-10, 07:06 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
The "Common" wire can be grounded.

Guessing they were not able to run a new wire outside, so that's why they did it.. I've done it once before in the past where fishing a new wire was going to be very hard.
 
  #9  
Old 11-03-10, 08:11 AM
A
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
So this grounded blue wire will have no effect on the staging/efficiency/operation of the unit? I paid a good amount of money for the system, and I know the installer would come back out if I wasn't satisfied, so if you think I should have them connect it to the AH, I will.

Also, in the installers test mode when I cycle stage 1 and stage 2 of the compressor should there be a clear audible change?


Thanks
 
  #10  
Old 11-03-10, 09:03 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by adoyle1 View Post
So this grounded blue wire will have no effect on the staging/efficiency/operation of the unit?
No, common wire will end up being grounded down the line.


Also, in the installers test mode when I cycle stage 1 and stage 2 of the compressor should there be a clear audible change?
I have not been around this unit in person, so I couldn't say for sure. You may notice it a little bit quieter, and fan running a little slower outside on 1st stage. Only best thing to tell is put an amp meter on the line, or count how long it takes for your house meter to spin around.
 
  #11  
Old 11-03-10, 12:48 PM
A
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 6
Received 0 Votes on 0 Posts
I found the wiring schematic for both the CU and AH and indeed it is grounded down the line at the AH. Just one more thing for my own sanity...If i meter the blue wire that is currently grounded (obviously disconnected from the ground), it would read +24 volts coming out?


Again Jay, thanks so much for your help.
 
  #12  
Old 11-03-10, 03:48 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
No, you won't get a reading 24 volts on common wire to ground.
 
 