Old York to New Honeywell TH5220D1003 Thermostat wiring help

I have an old York thermostat that is the slide left/right control with mercury. I recently purchased a New Honeywell TH5220D1003 thermostat to replace it with. I have a 2 heat / 1 cool heat pump setup and a Goodman outside unit. On the York the wiring is as follows...

LETTERING = WIRING FROM WALL

W = WHITE/BROWN (1 white wire and 1 brown wire)
B = BLUE
G = GREEN
R = RED
O = ORANGE
Y = YELLOW

On the Honeywell, the connections are as follows...

L
E
AUX
G
O/B
C
Y
R
RC (there is a jumper between R and Rc)


I think I have it pretty much figured out except to where to go with the white and brown wires as there is no "W" on the heat pump side of the Honeywell connectors. Here is how I "think" it might go...

Honeywell Connections = Wires from wall

L =
E =
AUX =
G = GREEN
O/B = ORANGE
C = Wont use as I will put batteries in)
Y = YELLOW
R = RED
Rc = Remove jumper from R/Rc


Thanks for your help as it is greatly appreciated!!!
 
Sponsored Links
  #2  
Old 11-21-10, 02:50 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by EZridaz View Post
I have a 2 heat / 1 cool heat pump setup and a Goodman outside unit.
What is your back up heat? Gas or electric? How many stages are they? Before we wire this up, I need this info.


Old----------------------New
W = WHITE/BROWN---Aux/E (Where does the White and brown wire go to at the furnace/air handler?)
B = BLUE---------------C
G = GREEN-------------G
R = RED----------------R/Rc
O = ORANGE-----------O/B
Y = YELLOW-------------Y
 
  #3  
Old 11-21-10, 04:15 PM
EZridaz's Avatar
Member
Thread Starter
Join Date: Aug 2006
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Thanks for the reply Jay!

Everything is electric. Here is what I saw on the Goodman Model# PH036-10...


C = BLUE
Y = YELLOW
E = BROWN
W2 = WHITE
O = ORANGE
G = GREEN
R = RED

When I connect the red wire to R or Rc, do I leave the jumper in place or take it off? Also, do I take the Blue wire off of "C" if I am running batteries in the thermostat? Thanks again!!!

edit...Will "Brown" go to "E" and "White" go to Aux on new tstat?
 

Last edited by EZridaz; 11-21-10 at 05:01 PM.
  #4  
Old 11-21-10, 05:42 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Originally Posted by EZridaz View Post
Thanks for the reply Jay!
Glad to help.
HP-------------Stat
C = BLUE------C
Y = YELLOW---Y
E = BROWN----E
W2 = WHITE---Aux
O = ORANGE---O/B
G = GREEN-----G
R = RED--------R/Rc (leave jumper. You can hook it up to either one)

Also, do I take the Blue wire off of "C" if I am running batteries in the thermostat?
I'd use the system power.. No need for the battery since this is not a program stat.

Installer set up menu.
1-5
2-0
3-1
6-3
8-3
9-2
12- up to you.
26-0
 
  #5  
Old 11-21-10, 06:57 PM
EZridaz's Avatar
Member
Thread Starter
Join Date: Aug 2006
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Thanks a million Jay....I greatly appreciate your time and help!!!!

I got it all hooked up and went through all the "System Test" and seems to be doing what it is suppose to!

I did have a question, more food for thought I guess...

1. On the setup it didn't give me #3 but in #6 and #8 would I want to put #6-9 and #8-9 for electric rather than "Hot Water Systems"? I saw where it also said ..."furnaces over 90% efficiency", but didn't know if that was for water systems only or any. Thanks again....your a life saver!!!
 
  #6  
Old 11-21-10, 07:01 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
Setting it to 9 CPH (Cycle per hour) is too much of "on and off" cycle, and that can be hard on the equipment, and if you were running electric heat only, it don't get a chance to "warm" up.

3 give you better comfort.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: