Booster fan hook up


  #1  
Old 11-28-10, 04:07 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
Booster fan hook up

I installed an in line booster fan in my duct to bring more hot air into my "cold" room.

Got a relay, hooked it up in such a way that when I jump two low voltage wires on it the

relay closes and my fan works.

My question is how do I hook it up to my existing forced air system?

Can I use my digital low voltage thermostat?

My system is 4 wires one stage heat/cool.

I will appreciate any help.

Paule
 
  #2  
Old 11-28-10, 05:55 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
If this is this connecting to a gas furnace, I recommend a current sensing relay.

If this is connecting to an air handler with electric heat, using a stat configured for electric heat, wire G and C to your relay.
 
  #3  
Old 11-28-10, 07:04 PM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,491
Upvotes: 0
Received 8 Upvotes on 8 Posts
Booster fan will not work. You can't push air that is not there. You would be better off fixing the ductwork to provide the cfm needed to heat and cool that room
 
  #4  
Old 11-28-10, 08:05 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
Actually I'm using it allready for a month. I've connected it to a switch and when thermostat calls for heat I manually turn the switch on. My room warms up in no time now, there is a lot of hot air coming through the register with the help of my booster. But how can I make it work in fan auto mode?
 
  #5  
Old 11-28-10, 08:12 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
It is a gas furnace. I was planing to use G terminal on my thermostat but since my furnace blower is being hooked up to the same G terminal my booster works only in fan on position and doesn't work in fan auto. Also this type of hook up activates furnace bypassing thermostat and system is working on its own.
 
  #6  
Old 11-28-10, 08:25 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
A current sensing relay grabbing the heating speed fan wire.

 
  #7  
Old 11-28-10, 08:33 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
Would you be kind to explain that?
 
  #8  
Old 11-28-10, 08:52 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
I think I got it. This relay closes when senses current and can be used to activate my fan. Now is my other problem. My in-line fan is in the attic because it boosts up the air for bedroom on 2nd floor. My furnace is in the basement and to run wires from attic there... Forget about it. That's why I'm trying to see if I can use thermostat. Would this relay work of thermostat?
 
  #9  
Old 11-29-10, 05:27 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
If you have a digital stat...

You can wire the coil of a 24 volt fan relay to W and C at your stat.
Wire a 10 minute adjustable Delay On Make in series with the W signal to this fan relay. Measure the time it takes for the blower to start when heat demand is givin at the stat, and set your 10 minute delay a little after this.
 
  #10  
Old 11-30-10, 04:39 AM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
Can you tell me more about this adjustable delay?
 
  #11  
Old 11-30-10, 04:33 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
http://www.icmcontrols.com/downloads/icm102-ig.pdf

Interrupt the W circuit...

"When power is applied to the input, the time delays begins. After the time delay is complete, the load energizes and remains energized as long as power is applied."
 
  #12  
Old 11-30-10, 05:20 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'll try to get it done over the weekend and will let you know the results. Meanwile thanks a lot for your help. I really appreciate it.
 
  #13  
Old 12-01-10, 09:04 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
Do you have any extra wires between the stat and the furnace?
 
  #14  
Old 12-04-10, 03:50 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
I do have one extra wire between the stat and furnace.
 
  #15  
Old 12-04-10, 07:07 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
This is great, because we need common.
 
  #16  
Old 12-04-10, 07:43 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, I'm listening. What do you have in mind? As the matter of fact I've got time delay relay as you suggested, but didn't install it yet.
 
  #17  
Old 12-04-10, 11:17 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
  #18  
Old 12-05-10, 06:39 AM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
What is the box on the right with yellow and common terminals?
 
  #19  
Old 12-05-10, 10:28 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
AC (condenser).

Alright now, no dissing the artwork
 
  #20  
Old 12-05-10, 10:30 AM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
That'a a cooling unit. Is it?
So, I'll have to install time relay on break in series with white wire and provide common to the other leg of my fan relay low side setting time delay a bit after the main fan will kick in?
 
  #21  
Old 12-05-10, 10:33 AM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sorry, I never meant to offend you. As far as your artwork it is very nice.
 
  #22  
Old 12-05-10, 10:35 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
Yes, it is a cooling unit.
Yes we need Common and W to the new relay, and the new timer wires in series to the new relay's W signal.
 
  #23  
Old 12-05-10, 10:46 AM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
One more question. My system has 3 zones with automatic dampers and separate stat for each zone. The changes that we are making to one zone shouldn't affect two others?
 
  #24  
Old 12-05-10, 10:55 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
It will not affect the other zones.
What zone control board are you using?
Is it a EWC Ultrazone, Honeywell, or Carrier?
If you see Vg, V+, Rs+, and Rs- terminals at the stat that you want to wire to, this plan will not work.
 
  #25  
Old 12-05-10, 11:13 AM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have Honeywell board and haven't seen those terminals there.
Few weeks ago I replaced thermostat on one of my zones with wireless FocusPRO Honeywell unit and had to use the spare wire to provide common to the module receiver and it works fine.
I'll be away for two weeks, but as soon as I'm back I'll do this project and will let you know the results.
You can't imagine how greatfull I am for all your help. Thanks a lot, Paul.
 
  #26  
Old 12-05-10, 11:18 AM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
P.S. The thermostat that I'm using is Honeywell Vision Pro series and also doesn't have those terminals.
 
  #27  
Old 12-05-10, 11:35 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
That is an excellent stat.
I'd connect C to the stat and furnace, and pick up W and C from the stat terminals.
 
  #28  
Old 12-05-10, 12:13 PM
P
Member
Thread Starter
Join Date: Nov 2010
Location: US
Posts: 22
Upvotes: 0
Received 0 Upvotes on 0 Posts
That's what I'll do then.
 
 