Vision Pro 9000 & outdoor temp sensor ...

I have a TH9421C 1004 thermostat with EMI and Tru Steam humidifier. I want to install an outdoor temp sensor - C7089U 1006 You opined that it would probably work if I ran the sensor wires within the heat pump cabling, using spare wires - thank you!
The sensor instructions say to attach to S1 &S2 inside the thermostat - but there are no such points within the VisionPro 9000 !!!! (only 3 wires going to the EMI) My question ... where do I hookup the 2 wires from the sensor to the system?

Once again, thank you for your help!
Bob
 

Last edited by hvactechfw; 04-07-11 at 03:24 PM. Reason: MERGED 2 THREADS WITH SAME EXACT QUESTION
Sponsored Links
  #2  
Old 04-07-11, 03:25 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,245
Received 2 Votes on 2 Posts
they connect to the out terminals in the EIM.
 
  #3  
Old 04-08-11, 07:22 AM
Member
Thread Starter
Join Date: Aug 2010
Location: Canada
Posts: 33
Received 0 Votes on 0 Posts
Thank you - the diagram is especially helpful !!!
 