Hello, again. It seems I keep coming back here to bother you guys with my troubles :/

I am replacing a faulty RiteTemp thermostat with a new Filtrete 3M-50. Upon removal of the existing unit, I found Y, G, R, and W wires. I thought myself lucky when I noticed an unused blue wire wrapped around the sheath, and figured I'd use it as a C wire, which I need for the WiFi module on the new unit.

Back on the furnace, however, I found no neatly organized terminal block with labeled wires, but rather a bunch of loose wires connected with wire nuts. The blue wire was wrapped the same way on this end, but I had no idea where to connect it.

I then noticed an unused purple wire coming from the handler. I thought I might get lucky and have that power the C terminal, so I used a wire nut to splice the blue to the purple. I'm a bit apprehensive about the whole thing though, so I've yet to connect the other end back on the thermostat for fear of causing irreparable damage.

Any idea what this purple wire is meant for, and would I be able to use it for my intended purposes? If not, is there a way for me to conjure up a C wire connection with the existing wiring?

Thank you guys for all your advice. Your help is more valuable than you can imagine.
 
Attached Images   
Sponsored Links
  #2  
Old 10-16-12, 11:01 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,384
Received 11 Votes on 9 Posts
24vac common is the brown wire from the transformer shown on the right side of your picture. (not the brown capacitor wires)

It is next to the red 24VAC wire on the transformer.


Purple is electric heat strip.
 
  #3  
Old 10-16-12, 11:02 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
Your picture of the wiring diagram is too fuzzy for me to really be certain but I'm pretty sure that violet wire is incorrect. You CAN just connect the blue thermostat wire to the chassis and it will be correct for the thermostat C connection.
 
  #4  
Old 10-16-12, 11:56 PM
alfredog83's Avatar
Member
Thread Starter
Join Date: Oct 2012
Location: United States
Posts: 8
Received 0 Votes on 0 Posts
24vac common is the brown wire from the transformer shown on the right side of your picture.
That brown is connected to a yellow wire, which is not connected to any terminal on the thermostat but rather some other mystery wire back at the receptacle. There is another black wire from elsewhere connected to the thermostat's Y terminal. Does that change things at all?
You CAN just connect the blue thermostat wire to the chassis and it will be correct for the thermostat C connection.
The diagram shows the brown wire Houston mentioned being connected to a GND screw. Is this why connecting the blue thermostat wire to the chassis would result in a correct connection?
 
  #5  
Old 10-17-12, 12:39 AM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
The diagram shows the brown wire Houston mentioned being connected to a GND screw. Is this why connecting the blue thermostat wire to the chassis would result in a correct connection?
Yes, that is the reason. jhiogyufgio;
 
  #6  
Old 10-17-12, 12:43 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,582
Received 416 Votes on 389 Posts
According to the schematic you gave us, the brown wire which comes from the 24vac transformer connects directly to ground (cabinet). In your photo I see the yellow thermostat wire going to the brown. That would seem to suggest that you have C at your t'stat location. In your last post you talk about receptacle. You've lost me there.
 
  #7  
Old 10-17-12, 06:34 AM
alfredog83's Avatar
Member
Thread Starter
Join Date: Oct 2012
Location: United States
Posts: 8
Received 0 Votes on 0 Posts
In your last post you talk about receptacle. You've lost me there.
Sorry, the wording in that post is a bit confusing. What I meant is that back at the thermostat location, that yellow wire is connected to another wire rather than one of the t'stat terminals, and back out into the conduit. If I'm reading the schematic correctly, this seems to be going to the OD unit.
 
  #8  
Old 10-17-12, 08:38 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,582
Received 416 Votes on 389 Posts
Ok......so what's the problem ? The yellow wire is common and arrives at the back of the thermostat. If you want to use the blue wire also as a common connect it together with the yellow at the transformer location.
 
  #9  
Old 10-17-12, 08:45 AM
alfredog83's Avatar
Member
Thread Starter
Join Date: Oct 2012
Location: United States
Posts: 8
Received 0 Votes on 0 Posts
Ok......so what's the problem ? The yellow wire is common and arrives at the back of the thermostat. If you want to use the blue wire also as a common connect it together with the yellow at the transformer location.
I suppose I just wanted to make sure that tapping into it wouldn't cause any problems elsewhere. Thanks for your help, guys!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: