Installing Honeywell RTH7600 Thermostat

Hi all, looking for some help on wiring. I currently have an "Environments for Living" thermostat (no model # on unit) and attempting to install a Honeywell RTH7600 Thermostat.

The current thermostat is on top, while the new Honeywell is at the bottom.

So I guess if I match up all the letters that are on both of 'em it comes out as

(old --- new)
Y1 --- Y
G --- G
FD --- ???
T --- ???
To --- ???
W2 --- W2
C --- C
R --- R


So I don't know where FD, T, and To go... or at least that's what I assume?

Any help would be greatly appreciated!


 
Attached Images  
  #2  
Old 01-04-13, 08:15 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
I looked this up, and I am not coming back to anything for this stat??

Nothing at all on the back of it?

ANyway, going to need you give us more info, I am guessing you have a Heat Pump? Gas or electric back up heat?

You may have to go back to the furnace/air handler and see where those wires go to.
 
  #3  
Old 01-04-13, 11:14 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Post a picture of both sides of the part of the thermostat that you pulled off of the wall.

Probably has a Lennox part number on it.
 
  #4  
Old 01-05-13, 10:25 AM
A
Member
Thread Starter
Join Date: Jan 2013
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Hi Jay, Houston. Thanks for the quick response!


Don't know why it didn't occur to me to look at the serial(!). I just looked up the name on the front and it came up blank. Anyway, on the back it says Erv 24Super.....which I believe is this:


ERV-24-HC11 Thermostat With FanCycler | SCI USA


I don't know. We just recently moved in and couldn't figure out the controls, which is why I got this new thermostat. Now that we have the manual, maybe I should just leave it?
Uhm... To be honest Jay, I'm an idiot at this and can't even answer your question re: heat pump. We have an hvac up front (see attached). I assume its gas since I live in Northern California and have never lived anywhere with electric heat.

Check out my photos!
 
  #5  
Old 01-05-13, 12:45 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Your existing thermostat has 2 remote sensors (T and To) and a fresh air damper (FD) connected to it that your new stat will not support.

You will be losing these features with the new thermostat.



What are the dip switch settings?
 
  #6  
Old 01-05-13, 01:09 PM
A
Member
Thread Starter
Join Date: Jan 2013
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Thanks again!Houston!

Settings are 1-0-0-0-0-1

Uhr.... I guess I should just leave the current thermostat as is then??

I guess me and the mrs can just try to get used to it. Heh, never seemed to have much trouble figuring out a thermostat up til now. :/
 
  #7  
Old 01-05-13, 01:27 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Seems like you aren't using the remote sensors with those settings.

I'd wait until a Honeywell IAQ or a Honeywell Prestige IAQ is in the budget to replace the old stat so that I wouldn't lose features.

Amazon.com: Honeywell, Inc. Prestige Hd 2-Wire Iaq Kit: Home Improvement
 
  #8  
Old 01-05-13, 07:52 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 18,427
Received 0 Votes on 0 Posts
From your mode# on the outdoor unit, you have A/C, but I don't see anything on the inside unit.

The W1 not being wired up now and just W2, your heat is not going to come on right away, should be to W1.
 
 