Replacing programmable with manual thermostat
#1
Member
Thread Starter
Join Date: May 2010
Location: Canada
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Replacing programmable with manual thermostat
Hi & thank you in advance.
I have a Sears model EF16J2200A2 furnace that is hooked to a Sears model C387-47146 thermostat. I believe the thermostat has malfunctioned as the house temperature has climbed to 22C despite the t-stat being set to 17C and it won't turn off even when i switch the t-stat to off. I had to throw the breaker to stop the furnace. I have a manual Dimplex TS321W t-stat that I would like to install temporarily to have the furnace functional until I can get a replacement programmable t-stat (and also to verify the t-stat is the problem).
Now the issue I have is that there are 4 wires (R,W,Y & G) connected to the Sears t-stat & the Dimplex only has 2 wires (Red-Line & Black-Load). Is this switch possible and if so which wires do I hook up?
I have a Sears model EF16J2200A2 furnace that is hooked to a Sears model C387-47146 thermostat. I believe the thermostat has malfunctioned as the house temperature has climbed to 22C despite the t-stat being set to 17C and it won't turn off even when i switch the t-stat to off. I had to throw the breaker to stop the furnace. I have a manual Dimplex TS321W t-stat that I would like to install temporarily to have the furnace functional until I can get a replacement programmable t-stat (and also to verify the t-stat is the problem).
Now the issue I have is that there are 4 wires (R,W,Y & G) connected to the Sears t-stat & the Dimplex only has 2 wires (Red-Line & Black-Load). Is this switch possible and if so which wires do I hook up?
#3
Air handlers overshooting the heating setpoints often have a sticking heat sequencer.
Does the heat continue to run when you remove W on the existing stat?
Does the heat continue to run when you remove W on the existing stat?