Honeywell Thermostat RTH7600D Function 190 quick question ??

I have been worrying over this thermostat replacement all weekend. Thank you for responding with the other information... I think I have finally gotten everything wired correctly but have one last problem.

When I put the function 190 at one setting- the heat comes on but the air blows warm. When I put it at the other setting, the air blows cold and the heat does nothing-- it doesn't come on at all. This is my wiring:
Name:  photo 2.jpg
Views: 4618
Size:  28.1 KBName:  photo 1.jpg
Views: 3661
Size:  25.4 KB

Am I doing something else wrong?
 
  #2  
Old 10-12-13, 06:30 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
I believe 190 is the reversing valve setting for the heatpump. It only has two choices.... try changing it to the other choice and see if that takes care of the issue.
 
 