Honeywell RTH9580 WiFi thermostat on an old oil burner furnace?

I am wanting to install a Honeywell RTH9580 WiFi thermostat on my old oil furnace. It needs the C wire for 24v common. My furnace has a Honeywell R8184G 4009 protectorelay oil burner control which has 2 wires connected to the T terminals going to the old thermostat. I have ran a new 7 wire bundle (for future replacement of furnace). There is a transformer that has Y,W,C,G,R terminals on it, and the C&G have black wires connected running back into an electrical box. I guess my question is can I use that C connection To run the thermostat or am I going to have to put some kind of relay on to the T terminals?

Thanks for any help
Travis
 
Attached Images   
  #2  
Old 01-30-14, 03:46 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,521
Received 94 Upvotes on 87 Posts
I would connect the fan center R and C to the stat R and C.
Connect the stat Rh and W to the furnace T and T terminals.
Remove the jumper between Rh and R at the stat.
 
  #3  
Old 11-21-14, 08:36 AM
Z
Member
Join Date: Nov 2014
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Oil burner

I have the same setup can u post a pic of your wiring or even a wire diagram. I am not sure on your hook up you listed above?
 
  #4  
Old 11-21-14, 08:59 AM
Shadeladie's Avatar
Super Moderator
Join Date: Jan 2005
Location: PA - USA
Posts: 4,905
Received 391 Upvotes on 319 Posts
Hello and welcome to the forum! Travis has never returned to the forum so will not reply. You may want to start a new thread with any questions you have, so that someone else may help you!
 
  #5  
Old 10-18-15, 02:42 PM
A
Member
Join Date: Oct 2015
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
RTH9580WF thermostat to R8184G furnace controller.

I was just able to connect my RTH9580WF thermostat to my furnace with a R8184G controller. There are only 4 terminals on the controller T, T, F, F.
The F, F terminals are for the CS cell but it uses the common side of the 24V transformer.
If you connect the wires up to the terminals in this order it should work fine

T T F F
R W - B

Connect the Red to the outer T terminal and the Blue to the outer F terminal and the White to the remaining T terminal.
 
  #6  
Old 10-18-15, 02:56 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Welcome to the forums.

Thanks for the info and I'll add this diagram to what you've posted.

Name:  R8184G diagram.jpg
Views: 23379
Size:  22.2 KB
 

Last edited by PJmax; 10-18-15 at 03:13 PM.
  #7  
Old 09-28-17, 08:09 PM
A
Member
Join Date: Sep 2017
Location: USA
Posts: 0
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have the same issue. R8184G and looking to add a C wire for a smart thermostat.

Found this and figured I was set.

Kept doing some digging and found a thread on another forum where members basically said you're going to complete mess with the flame sensor by doing this:

**********
Thoughts?
 