New thermostat / conventional furnace with damper zone help

Reply

  #1  
Old 02-22-14, 08:36 AM
J
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
New thermostat / conventional furnace with damper zone help

I'm trying to swap out a circa 1996 Honeywell Trol-A-Temp thermostat with a new Honeywell Vision Pro8000 (TH8110R1008) thermostat. It a conventional furnace system with dampers controlling the 2 zones. The old Main thermostat has six wires. G, R, W, Y, B, O . No common. There's a slave thermostat for the zone upstairs with just three wires. Problem is with the "B" and "o" wires. The new thermostat has a combined B/O terminal (supposedly for heat pump system). The same terminal is used for the W heat in a conventional system. Here's a link to the wiring diagram http://hwll.co/q/VPROlit . Page 117. I called Honeywell support to decipher the puzzle but they wouldn't even talk to me because I wasn't a licensed professional. I couldn't even get out of them whether this thermostat would work on this system. "No Comment" . Any help would be appreciated. I can't believe this thermostat wouldn't work with all it's programmable technology.
 
  #2  
Old 02-22-14, 08:56 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
  #3  
Old 02-23-14, 05:36 AM
J
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
I have an extra wire to use as the common "C". Why do I need the fan relay and how do I wire it and the thermostat? Thanks.
 
  #4  
Old 02-23-14, 11:24 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
A relay can be used to overcome the issue with a single terminal for O and B but it will not help with the fact that you have a single stage TH8110 thermostat.

The TH8320 or TH8321 could be used with a relay but the heat setpoint would be 2 degrees off.

I would look into White Rodgers thermostats for your application.
 
  #5  
Old 02-23-14, 11:35 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Looks like White Rodgers also uses an O/B terminal with their WiFi stat...

http://www.emersonclimate.com/Docume...or_website.pdf
 
 