Ran the delta t on heat pump heat again today not sure if these readings will help you since outside temp was so warm.
Outside Temp :59 degrees
Before Fan speed change (1200 cfm high/ 780 cfm Lo)
Discharge:97 degrees Return: 72 degrees Delta: 25 degrees
10 minutes of fan running with no call for heat then sat 10 minutes
Change to new fan speed setting (1080 cfm high / 702 cfm lo)
Discharge: 106 degrees Return: 76 degrees Delta: 28 degrees
  #42
Old 04-01-14, 07:14 PM
Houston204's Avatar
Received 17 Votes on 14 Posts
The heat delta Tee looks good.
The cooling delta Tee might be another story.
  #43
Old 04-01-14, 10:18 PM
R
We are suppose to get some 70 degree days this week so I will run it then and get the readings
  #44
Old 04-04-14, 11:22 AM
R
Outside Temp 71 degrees
Starting Discharge: 67 degrees Return 68 degrees
Ending Discharge 48 degrees Return 66 degrees Delta 18
  #45
Old 04-05-14, 08:07 AM
Houston204's Avatar
I like 18 degree splits. Are you still set for 1200 CFM?
  #46
Old 04-05-14, 10:09 AM
R
No I had already changed it before I ran the heating tests. It is set to A-C (1080 cfm high / 702 cfm lo)
Is that a bad thing?
  #47
Old 04-05-14, 10:36 AM
Houston204's Avatar
1200 cfm could cause high humidity problems with a 2.5 ton outdoor unit.
You have the correct setting.