Need Wiring Assistance.


  #1  
Old 04-25-14, 09:51 PM
N
Member
Thread Starter
Join Date: Apr 2014
Posts: 1
Received 0 Votes on 0 Posts
Need Wiring Assistance.

Just bought a home that is using a York split system Heat pump with the maximizer add-on coil. It is using a thermostat Q674L 1272. The wiring is O, Y, X, R, G, B, W. There is also three wires that are not being used. I am installing the Honeywell RTH6580WF. For heat pump systems Honeywell uses R, RC (connected with jumper), Y, C, O/B, G, Aux/E, L, K.

Currently I have it wired
Old New
O O
Y Y
X Aux/E
R R
G G
B C
W Aux/E
L
K
I have read mixed messages about W, B and X. Some say to Taped off W. Some say X should be in the C slot. Other says B should be taped off. Any assistance would be greatly appreciated.
 
  #2  
Old 04-26-14, 02:16 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Color codes vary but I agree with your wiring. Down here I would tape off X but if I were in a colder area I would connect it to Aux/E along with the old W wire as you have.

http://i151.photobucket.com/albums/s...lQ674L1272.jpg
 
 