Honeywell Vision Pro 8000 wiring installation

Hi everyone,

I replaced a Honeywell Vision Pro 8000 thermostat recently with a unit I bought off Amazon. The new unit has wiring that was slightly different from my previous one. The old wall plate had separate "Aux" and "E" terminals and white and black colored wires going into each respective terminal. The new wall plate has a Aux/E terminal and I inserted both wires into this terminal. Everything seems to be working ok so far, but am I doing this right? Thanks.

DT
 
Attached Images  
  #2  
Old 05-30-14, 05:16 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: United States
Posts: 5,049
Received 91 Votes on 86 Posts
It would help to know what the new Tstat is.
Geo
 
  #3  
Old 05-31-14, 07:05 AM
D
Member
Thread Starter
Join Date: May 2014
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
sorry forgot to mention that they are both vision pro 8000s. Just that the new unit has a slightly different mounting plate...
 
  #4  
Old 05-31-14, 09:06 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
The new wall plate has a Aux/E terminal and I inserted both wires into this terminal. Everything seems to be working ok so far, but am I doing this right?
Yes your wiring is fine. Did you set function 170 to 7 to match your heat pump with Aux heat system?
 
 