Installing Honeywell RTH6350D


  #1  
Old 06-02-14, 08:33 AM
A
Member
Thread Starter
Join Date: Jun 2014
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Installing Honeywell RTH6350D

I'm switching over to the Honeywell from a Lennox 21J7201 T-stat. My outdoor unit is a Lennox 10HPB48-9. The old Tstat had the following wires:

R
W1
Y1
O
C
G

I hooked up the wires to the Honeywell as follows under "heat pump"

R - R with jumper to Rc
Y1 - Y
O - O/B
G - G
C - unconnected
W1 - Aux/E

When I turn the cold on, only warm air blows but I can hear the outside unit and compressor running. Is this Tstat compatible with my unit and did I hook it up correctly?
 
  #2  
Old 06-02-14, 04:36 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
You must also configure function 1 to 5 for Heat pump with Aux heat.

http://i151.photobucket.com/albums/s...HonRTH6350.jpg
 
  #3  
Old 06-03-14, 06:02 AM
A
Member
Thread Starter
Join Date: Jun 2014
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
That did it, guess I used the wrong program. Thanks a lot.
 
 