Hey

Just purchased two Honeywell RTH7600D thermostats to replace old White-Rogers units. I am starting with my downstairs unit and have a question. The old thermostat had 4 wires (W, RH, G, Y), these are self explanatory on the new one. There is also a fifth wire in the wall that's not being used (Blue). I went down to the furnace board and saw that the blue wire is not being used on the furnace side as well. There are two groups of wires coming out of the furnace board (W, RH, G, Y, Blue) going to thermostat, and (White, Red) going to AC. The White going to the AC is connected to COM on furnace, the Red is connected to "Y" on furnace.

My question is can i also hook the blue wire into the "COM" and furnace and use this as a "C" wire on the new thermostat?

Pics:




 
  #2  
Old 07-30-14, 04:50 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,159
Received 69 Votes on 61 Posts
FYI I approved your post..

Welcome to the forums.....

New members need so many posts before they approve automatically. This is because of links or pictures that our spam system thinks is spam..

A pro will be with you shortly to answer your questions...

 
  #3  
Old 07-30-14, 04:51 PM
H
Member
Thread Starter
Join Date: Jul 2014
Posts: 3
Received 0 Votes on 0 Posts
Thank You, I may have accidentally tried to post this twice. Please delete the second one.

Thanks
 
  #4  
Old 07-30-14, 04:56 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,159
Received 69 Votes on 61 Posts
My question is can i also hook the blue wire into the "COM" and furnace and use this as a "C" wire on the new thermostat?

Im pretty sure you can, as that is the only way really you will get 24v to the T stat.... But let one of the HVAC pros confirm this...

( I would have probably tried it already... But I know some of those stats are $$$$)
 
  #5  
Old 07-30-14, 05:07 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,193
Received 1,530 Votes on 1,413 Posts
My question is can i also hook the blue wire into the "COM" and furnace and use this as a "C" wire on the new thermostat?
You certainly can. There will be two wires on the C terminal which is fine.
 
  #6  
Old 07-30-14, 06:55 PM
H
Member
Thread Starter
Join Date: Jul 2014
Posts: 3
Received 0 Votes on 0 Posts
Thanks Guys, worked like a charm. I will do the upstairs tomorrow. Its a heat pump thermostat so I'll investigate how its wired and ask any questions if I have any.
 
 