Wiring Problem for Honeywell RTH9580WF1005 Smart Thermostat


  #1  
Old 09-26-14, 05:47 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
Exclamation Wiring Problem for Honeywell RTH9580WF1005 Smart Thermostat

I am looking to upgrade my current thermostat to this newer Honeywell Smart Thermostat. My problem is that I currently do not have a C wire at the thermostat unit. In addition, once i open the control panel at the furnace unit, i see that there is no Y wire connected to the Y terminal (But there is a Y wire at the terminal in the wall unit). Is it possible to still upgrade to the new thermostat or do i have to rewire the entire system? Its very weird how the wiring does not match from the poles at the wall unit to the furnace. i will include pictures for further explanation. any help will be appreciated.

Name:  get-attachment (1).jpg
Views: 815
Size:  24.9 KB

Name:  get-attachment (2).jpg
Views: 1054
Size:  37.4 KB

Name:  get-attachment.jpg
Views: 690
Size:  26.9 KB
 

Last edited by PJmax; 09-26-14 at 06:03 PM. Reason: reoriented/enhanced second picture
  #2  
Old 09-26-14, 05:56 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,726
Received 2 Votes on 2 Posts
It appears that whomever wired the two wires going outside to the a/c condenser did not use the Y terminal at the control board. They wire nutted the black wire from the Y terminal at 'stat to the red wire going out to condenser. The white wire on the C terminal at the control board goes outside with the red wire to provide control voltage to the contactor at the a/c condenser. To get a C wire at the thermostat the best method is to run a new thermostat cable. If that is too difficult to run you can use an external transformer to power the C wire.
 
  #3  
Old 09-26-14, 05:59 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
More information. The thermostat is for heating (gas) and cooling. Model is a Goodman. works fine but i want to upgrade the thermostat and need some answers before i do it.

thanks again,

Edgar
 
  #4  
Old 09-26-14, 06:03 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
Thanks for the help, Honeywell says that i can get away with substituting the C wire with the G wire. I would just lost fan control for recirculation. but they also state that i need to make a jumper connection between the Y and G terminals at the control panel. Will that still work without having a Y terminal hooked in to begin with?
 
  #5  
Old 09-26-14, 06:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,593
Received 1,601 Votes on 1,475 Posts
The Y terminal is just a splice point. So whether it's on the board or under a wirenut... it will work.

When you go to put your second wire under the C terminal you'll know why they used a wirenut.
 
  #6  
Old 09-26-14, 06:11 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
Thanks for the help, so if i were to make a jumper between the Y and G terminals like honeywell is saying to do, would that still work?
 
  #7  
Old 09-26-14, 06:16 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,593
Received 1,601 Votes on 1,475 Posts
Yup... that would work fine as the furnace will turn the blower on when it's warm and the call for A/C will turn on the fan and condensor at the same time.


PS... welcome to the forums. Also... your same question was removed from the other thread.
 
  #8  
Old 09-26-14, 06:24 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
Thanks for the help, i appreciate it.
 
  #9  
Old 09-26-14, 06:33 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
I also had another question. If i take the G wire and put it on C terminal like honeywell is saying to do, is it alright to have that C terminal at the control board double wired?
 
  #10  
Old 09-26-14, 06:49 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Yes it is okay to have the thermostat C and the condenser C on the Furnace C terminal.

What is the model number of your Goodman furnace?

I would connect the two Y wires to the furnace Y terminal. This increases blower speed in cool mode with some furnaces. A model number might allow us to view the furnace manual.
 
  #11  
Old 09-29-14, 01:20 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
Hello again, I installed the thermostat today according to the instructions and including the switching of wire G and C wires as well as the jumper between Y and G. Upon testing, Heating cycle works good everything running. upon A.C. testing, the unit outside the house starts up but no blower unit inside the house. Please advise.
 
  #12  
Old 09-29-14, 01:36 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
The jumper between Y and G only works when the stat Y is connected to the furnace Y terminal.
 
  #13  
Old 09-29-14, 02:04 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
HOUSTON WE HAVE A PROBLEM hahaha sorry couldn't resist....SO to recap, attach Y coming from t-stat to Y terminal at furnace control board correct? next question, what do i do with the other red wire that the Y that is coming from the t-stat is wire nutted to? i was having fun up until 30 minutes ago when i started playing with this thing.
 
  #14  
Old 09-29-14, 02:18 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
Name:  get-attachment (3).jpg
Views: 660
Size:  34.9 KB

also i believe the model number to my unit is

GCS90703BXA
Goodman, Natural gas forced air.
 
  #15  
Old 09-29-14, 02:30 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Stat Y and condenser Y connect to furnace Y.
 
  #16  
Old 09-29-14, 02:32 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,726
Received 2 Votes on 2 Posts
You should have two wires on the Y terminal at the furnace. One comes from the thermostat and the red wire that goes outside to the a/c condenser should also be on this Y terminal.

Edit: Houston204 and I provided the same info but he beat me to the punch. LOL
 
  #17  
Old 09-29-14, 02:36 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
Got it.....I am going to have 3 wires into that Y terminal at the furnace. I'm not in violation of some HVAC code or anything am I?
 
  #18  
Old 09-29-14, 03:32 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Nope, you are in good shape.
 
  #19  
Old 09-29-14, 05:13 PM
E
Member
Thread Starter
Join Date: Sep 2014
Location: United States
Posts: 21
Received 0 Votes on 0 Posts
Thank you fellas, we are up and running normally.

Thanks for all your help and patience with me.

Ed
 
 