Gree PTHP wiring to White Rodgers UP300 programmable T-stat


  #1  
Old 10-19-14, 08:29 PM
F
Member
Thread Starter
Join Date: Oct 2014
Location: Canada
Posts: 4
Received 0 Votes on 0 Posts
Gree PTHP wiring to White Rodgers UP300 programmable T-stat

Hi,

I live in an apartment with PTAC units and remote T-stats, my PTAC unit died so I replaced it with a new Gree PTHP but my existing T-stat was not compatible with the heat pump.

There is a ten wire harness in the wall to the PTHP so I knew I could get a new T-stat and wire it up. I bought the White Rodgers UP300 to use and wired it up but the PTHP only uses the electric resitance heat when in heat mode.

The PTHP has the following connections:
R - 24 VAC
W - Electric/Heat
Y - Compressor
O - Reversing Valve
GH - High Fan
GL - Low Fan
C - Common

The old PTAC had all of the wires connected except for the O. I connected the O to the new PTHP and then at the white rodgers T-stat I connected the following.

O----O
Y----Y
G----GL (I know the fan will operate in low mode)
Y Jumpered to W (W on the unit is not connected)
C----C
R----R

The old T-stat had Y, G, C, W, R connected.

Currently I left the W wire not connected to the white rodgers - do I need to connect it to the W2 as the second stat (electric heat)? I can clarify if this is confusing in any way. The old PTAC and T-stat were both Carrier models. Thanks in advance for the help.
 
  #2  
Old 10-20-14, 07:31 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 2,101
Received 0 Votes on 0 Posts
I would land the W wire on W at the stat. Leave the jumper in place. Have you set the switches on the back of the stat?
 
  #3  
Old 10-20-14, 09:02 AM
F
Member
Thread Starter
Join Date: Oct 2014
Location: Canada
Posts: 4
Received 0 Votes on 0 Posts
I tried putting the W wire in the W on the stat and got a wiring error status on the PTHP.

The switches are set to elec and "O"

The PTHP manual is here:
http://www.gree-etac.com/docs/Gree%20ETAC%20OM.PDF

I am going to try the W wire to W2 when I get home after work today.
 
  #4  
Old 10-20-14, 09:55 AM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,726
Received 2 Votes on 2 Posts
I bought the White Rodgers UP300 to use and wired it up but the PTHP only uses the electric resitance heat when in heat mode.
Did you set dip switches 1 and 2 on the unit? If dip switch 1 is set in the UP position only the electric strips will be used for heat. If it is set to the down position then the heat pump will provide first stage heating.

As Skaggsje stated, the W wire should be connected to the W terminal on the thermostat.
 
Attached Images  
  #5  
Old 10-20-14, 05:30 PM
F
Member
Thread Starter
Join Date: Oct 2014
Location: Canada
Posts: 4
Received 0 Votes on 0 Posts
Yes the dips are set right. I tried putting the w wire in the w but the pthp gave me an error status.
 
  #6  
Old 10-20-14, 06:10 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,726
Received 2 Votes on 2 Posts
Did you set thermostat Option 3 to On1 as outlined in section 3.3 of the installation manual:

http://www.emersonclimate.com/Docume.../0037-7256.pdf
 
  #7  
Old 10-20-14, 07:46 PM
F
Member
Thread Starter
Join Date: Oct 2014
Location: Canada
Posts: 4
Received 0 Votes on 0 Posts
Okay I got it working! Had to land the W wire into the W2 port on the tstat for backup heat.

Thanks everyone for the help!
 
  #8  
Old 10-20-14, 08:00 PM
firedawgsatx's Avatar
Member
Join Date: Jul 2013
Location: USA
Posts: 1,726
Received 2 Votes on 2 Posts
Glad to hear you got it working and thanks for letting us know. I was just getting ready to post an excerpt from a thermostat wiring diagram that showed the W wire going to W2 on a similar unit. (see attached)
 
Attached Images  

Last edited by firedawgsatx; 10-20-14 at 08:42 PM.
 