Hi,
I've found several threads on this base and some even going to Robertshaw but would like to get the mappings since none of them are perfectly matched to mine.
I wanting to go from Q674L 1272 to Robertshaw 9520 (old to slightly less old)
Handler - Wire - Q674L 1272
Y - Yellow - Y
O - Orange - O
X - Black - X
R - Red - R
G - Green - G
B - Tan - B
60 - White - W
The 9520 has
1st block
C
L
R
2nd block
Y2
Y1
E
G
W2
O
B
The setup is a heat pump with aux heat strips.
Not sure if this is the right number or not but handler shows g/hc018sa
Thanks
Old 11-08-14, 01:20 PM
Houston204's Avatar
Received 17 Votes on 14 Posts
The 9520
1st block
C = tan
L = not used
R = red
2nd block
Y2 = not used
Y1 = yellow
E = black
G = green
W2 = white
O = orange
B = not used
Old 11-09-14, 06:52 AM
K
Thanks a lot! It's all working great except emergency. I switch the tstat to emergency and the air feels cold where I expected it to smell/feel like aux does. Is that not how it should be?
Old 11-09-14, 08:58 AM
Houston204's Avatar
I'd place a jumper wire between W2 and E if you get no heat after giving the stat an emergency heat demand and waiting a few minutes for the sequencer to engage the heat strips.
Old 11-10-14, 05:51 AM
K
Would there be any potential side effects (wear and tear, efficiency/utility cost) with that or is that essentially the same thing that emergency should be doing anyways?
Old 11-10-14, 04:59 PM
Houston204's Avatar
It depends on the way the heat strips are wired and the heat strip size and the air handler size.
If you have a 10 KW heat strip all 10 should be energized for emergency heat. For that setup I would jumper Aux to E and tape off the old E wire.
If you have 20 KW, which is usually four elements, then you may have a bad sequencer, or fuse link for the 10 KW energized by the E terminal.
If you have a 15 KW heat strip, you may have 10 KW wired to Aux and only 5 KW wired to the E terminal. This would not produce much heat in emergency heat mode with an air handler much larger than 2 tons.
5 KW pulls around 20 amps, so 20 KW can be expensive to run. If you have an intermittent problem with a heat sequencer you could end up running 20 kW intermittently if you jumpered Aux to E and didn't tape off the old E wire.
If you post some pictures of the heat strip tag, the model number of the air handler, and wiring connections we can offer more accurate assistance.
Old 11-10-14, 08:12 PM
K
Here are some photos that will hopefully help.
Thinking about it today though, it may all be moot -
This heat pump handles what used to be a garage converted to living space and a room above that. So it doesn't have a whole lot of square feet to condition.
Considering that, I guess Emergency heat in this situation isn't a big deal as there would never be an emergency situation where I would have to have those two rooms heated. So that being said, I'll go ahead and post the photos as I appreciate your insight but feel free to put answering this one to the bottom of your undoubtedly long list.
Since it's 10, looks like I can just bridge Em to Aux and tape E as you suggested.
Size:  35.4 KBName:  IMG_20141110_214318_417.jpg
Size:  27.5 KBName:  IMG_20141110_214448_968.jpg
Size:  25.0 KBName:  IMG_20141110_214730_763.jpg
Size:  46.3 KBName:  IMG_20141110_214809_947.jpg
Size:  40.0 KBName:  IMG_20141110_214813_679.jpg
Size:  43.6 KBName:  IMG_20141110_214818_372.jpg
Old 11-10-14, 08:36 PM
Houston204's Avatar