Replacing Lennox thermostat with NEST w/ pictures.

Hello,

I have a Lennox Heat Pump (Model E16Q3-15-1P) using a Lennox mercury thermostat (Pt. No. 36G6901). I am looking for help in replacing the Lennox thermostat with the NEST from my previous home. The wires connected to the old thermostat are labeled R, V, F, M, L, A Y, X, and I am looking to convert them to the NEST labels. I have been able to find some posts on this forum where Houston204 broke down the wiring on a similar thermostat, but this one is just slightly different and I don't want to damage anything by assuming its the same.

Also, would I set the NEST to a specific single heat pump setting during setup?

Here is a pic of the old wiring
Name:  Lennox2.jpg
Views: 3867
Size:  41.1 KB

Here is a picture of the wiring on the heat pump in case it is useful. On a side note, I noticed there are two sets of wires which makes me wonder where the other set goes. I have read about outdoor sensors but I am not sure if this applies to my unit. I just bought the house and still poking around. I should make this a separate thread and ask about that.
Name:  Wiring1.jpg
Views: 2434
Size:  23.2 KB

The Furnace:
Name:  Lennox1.jpg
Views: 2503
Size:  37.8 KB

And finally, the NEST:
Name:  Nest.jpg
Views: 2456
Size:  29.1 KB

Thank you very much for taking the time to help me out. I really appreciate it.
 

Last edited by PJmax; 01-08-15 at 04:25 PM. Reason: cleaned up old t'stat pic
Sponsored Links
  #2  
Old 01-08-15, 04:14 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,350
Likes Received: 6


Lennox = your wire = Nest = function
R = black = O/B = reversing valve
V = blue = Rc = 24 volt power
F = green = G = fan
M = red = Y = compressor
L = brown = tape off = fault light
A = white = tape off = thermistor
Y = orange = Aux = heat strip
X = yellow = C = 24 volt common

Name:  nestwithHPwithauxheat.jpg
Views: 15783
Size:  31.9 KB
 
  #3  
Old 01-10-15, 12:53 PM
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 2
Thank you!

Thank you for your help! I have the NEST installed and it is working properly. It appears that I have a Heat Pump and Auxiliary furnace which was news to me. Thanks again and keep up the good work!
 
  #4  
Old 01-10-15, 03:55 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,350
Likes Received: 6
You are very welcome.

It took me a good while to make sense of this wire combination the first time that I came across it.

Someone had wired the heat pump with only Y and C for straight cooling and the homeowner removed the old stat and left it on a table along with a new stat for me to install.

These days smart phones and the internet is a great help for looking up diagrams.
 