Air handler blower will not shut off


  #1  
Old 01-14-16, 10:21 AM
L
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Received 0 Votes on 0 Posts
Air handler blower will not shut off

Greetings everyone, new to the forum.

I have a Goodman ARUF48601 handler, fan will not shut off. I have done some diagnostics based on other threads I have seen here on this forum and I still need assistance. Stat is a Honeywell RTH6350. Stat and handler board components (don't know exactly what) were replaced about 6 months ago by a local hvac company. Heat and cold work fine, but apparently the fan has always been on (I don't live there). Stat has auto and on for fan, no effect when changed. I researched the stat wiring, all appears correct. I can remove G from stat and it has no effect on the fan. Pulled the panel off the handler and put the meter to a few items I saw noted in other threads. G wire has 6 vac on it at all times. When stat fan is engaged, G goes to appropriate 24 vac. Measured EBTDR at C and R, shows 24 vac. Don't want to call hvac company that did the board repairs unless I can prove a warranty issue.

Any help is greatly appreciated!
 
  #2  
Old 01-14-16, 11:13 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,837
Received 1,476 Votes on 1,364 Posts
Welcome to the forums.

If you disconnect the stat from the air handler.... or at least the G connection..... and the blower still runs.... The timer board is defective or more likely a sequencer issue. Both can keep the blower running.

Click on pic for larger view.
 
  #3  
Old 01-14-16, 11:59 AM
L
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Received 0 Votes on 0 Posts
Thanks PJ. I had seen a similar thread where Houston replied with similar info. Is there a way to test the sequencer and timer board?
 
  #4  
Old 01-14-16, 04:43 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
The sequencer is sending high voltage From PLF3 on the harnes to the NC (normally closed) terminal on the EBTDR.

If you unplug that wire and the fan isn't stuck on anymore it would point to a sequencer problem.
 
  #5  
Old 01-14-16, 05:45 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,837
Received 1,476 Votes on 1,364 Posts
Oh...sorry. I posted the diagram and forgot to tell you what to do. Thanks Houston.
 
  #6  
Old 01-18-16, 12:56 PM
L
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Received 0 Votes on 0 Posts
Well, After verifying the the PLF3 wire removal did shut the blower off, I replaced the sequencer....blower still won't shut off. Any suggestions? Should I look at that Honeywell stat wiring any closer?
 
  #7  
Old 01-18-16, 04:59 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
The sequencer may be improperly wired or it may be getting 24 volts to the base.

PLM 3 should land on the same side of the sequencer as the heating element. If it is on the hot side of the sequencer the fan would never turn off.

We had another poster with this problem.

http://www.doityourself.com/forum/ai...-turn-off.html

If you post some pictures of the sequencer area we may be able to offer more detailed assistance.
 
  #8  
Old 01-19-16, 07:59 AM
L
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Received 0 Votes on 0 Posts
Pics as requested:
Name:  IMG_2048.jpg
Views: 725
Size:  32.8 KB
Name:  IMG_2042.jpg
Views: 689
Size:  34.8 KB
Name:  IMG_2043.jpg
Views: 683
Size:  31.7 KB
Name:  IMG_2044.jpg
Views: 684
Size:  36.9 KB
Name:  IMG_2045.jpg
Views: 703
Size:  30.2 KB
Name:  IMG_2046.jpg
Views: 672
Size:  30.3 KB
Name:  IMG_2049.jpg
Views: 684
Size:  50.7 KB
Name:  IMG_2051.jpg
Views: 852
Size:  47.6 KB
Name:  IMG_2050.jpg
Views: 739
Size:  26.1 KB
 
  #9  
Old 01-19-16, 10:19 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
That first picture is probably the key but it is dark. Do you own a drop light?
 
  #10  
Old 01-19-16, 10:56 AM
L
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Received 0 Votes on 0 Posts
See if this works Houston:
Name:  IMG_2052A.jpg
Views: 767
Size:  53.6 KB
Name:  IMG_2053B.jpg
Views: 756
Size:  48.2 KB
Name:  IMG_2054A.jpg
Views: 671
Size:  41.4 KB
 
  #11  
Old 01-19-16, 05:05 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
Yep, it looks like you gave the same problem.
Pink is on the wrong side of the sequencer.

It is on top along with the incoming power wire on that red wire nut with tape.

It should be on the other side that feeds the heating element.

I can give you arrows when I get home.
 
  #12  
Old 01-19-16, 06:12 PM
L
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Received 0 Votes on 0 Posts
Got it! ....Fixed !

You guys are awesome, really appreciate the help.

This culminates a very poor repair from a local and reputable HVAC contractor that wound up costing me initially an additional $1000 in electricity (no exaggeration) due to misdiagnosis (they didn't know the emer heat and cool was operating simultaneously) and now appx $300 in electricity over the past 7 months for the blower fan mis-wired. Nice....
 
  #13  
Old 01-19-16, 09:26 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,425
Received 17 Votes on 14 Posts
I am glad that you were able to resolve this problem with our assistance

Name:  Goodman ARUF Miswire.jpg
Views: 2005
Size:  49.3 KB
 

Last edited by Houston204; 01-19-16 at 09:48 PM.
 