Voltage to thermostat (r-wire) question


  #1  
Old 02-28-16, 09:09 AM
D
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 9
Received 0 Votes on 0 Posts
Voltage to thermostat (r-wire) question

I am trying to install an Ecobee3 programmable thermostat which requires 24VAC to operate. I have a Carrier Comfort 92 heating system.

The current thermostat operated fine, but wasn't programmable (Carrier TSTATCCBAC01-B, http://esmithair.com/wp-content/uplo...stallation.pdf). That thermostat had the following wires: W, O, G, R, C, Y. It should be compatible.

When I check the R-wire, I am only reading 5VAC. (According to the manual for this old thermostat, it also requires 24VAC so I am unsure how it is running on the 5VAC being provided.)

Any ideas on what may be causing this before I open up the furnace to look at the Furnace Control Board? Any help is greatly appreciated.
 

Last edited by db9908; 02-28-16 at 09:28 AM.
  #2  
Old 02-28-16, 11:08 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,853
Received 1,477 Votes on 1,365 Posts
Checking the R wire to what ?

You should be checking between R and C.
 
  #3  
Old 02-28-16, 11:14 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,853
Received 1,477 Votes on 1,365 Posts
This would be the code you would follow. No need to jumper Rh to Rc.

W -----> W1
O -----> O/B
G -----> G
R -----> Rh
C -----> C
Y -----> Y1
 
  #4  
Old 02-28-16, 03:01 PM
D
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 9
Received 0 Votes on 0 Posts
Hi, PJmax! Thanks for the reply. That is exactly how I wired it up and I was checking R to C which gave me the 5 VAC reading. From what I can tell looking at the diagram for the Carrier Comfort 92 it should be outputting 24VAC to the thermostat so I am confused as to why I'm only reading 5v there. I suppose I'm going to have to open the furnace to get access to the control board to take a reading there to verify output as the next step.
 
  #5  
Old 02-28-16, 03:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,853
Received 1,477 Votes on 1,365 Posts
If you did the wiring with the air handler on you probably blew a protection fuse on the control board. It's usually a 3 or 5 amp ATC automotive type fuse.


Name:  index.jpg
Views: 996
Size:  5.1 KB
 
  #6  
Old 02-28-16, 06:19 PM
D
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 9
Received 0 Votes on 0 Posts
Thanks, Pete! I will take a look at that tomorrow after work. Would fuse prevent the system from operating at all? Would it make the R-C read 5v?

The part that is really blowing my mind is that although the old thermostat documentation states that it is a 24V system, it still runs even though R-C only reads 5V. When I plug the old thermostat back in the whole system runs like a champ.

Weird.
 
  #7  
Old 02-28-16, 06:32 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,853
Received 1,477 Votes on 1,365 Posts
No.... if the fuse was blown..... the old stat would not work either.
Are you sure the meter is set for AC voltage..... not DC voltage ?
 
  #8  
Old 02-28-16, 06:38 PM
D
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 9
Received 0 Votes on 0 Posts
Yup. I have pretty good experience working with electronics. This is why I am so baffled.

Also, another indication I receive of low voltage is that when I wire up the Ecobee3 I hear a clicking sound but nothing comes on. The documentation for that system says this is an indication of low voltage.
 
  #9  
Old 02-28-16, 06:57 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,853
Received 1,477 Votes on 1,365 Posts
Your next step is to check at the control board. 24vac should be found between the blue and red.

Name:  92.JPG
Views: 1641
Size:  39.0 KB
 
  #10  
Old 02-28-16, 07:12 PM
D
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 9
Received 0 Votes on 0 Posts
I will take a reading there after work tomorrow and post what I get. Thanks for the diagram! I appreciate all the help!
 
  #11  
Old 03-01-16, 03:44 PM
D
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 9
Received 0 Votes on 0 Posts
Alright, Pete! I am even more confused now! Haha! Red to Blue on the Furnace Control Board reads 27VAC. Any ideas?
 
  #12  
Old 03-01-16, 04:28 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,853
Received 1,477 Votes on 1,365 Posts
Do the colors on those two terminals match the colors on the stat end ?
Possibly you have a splice in the line.
 
  #13  
Old 03-01-16, 06:05 PM
D
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 9
Received 0 Votes on 0 Posts
Good call. Didn't even dawn on me. The Blue wire on the Furnace Control Board is a Black wire at the thermostat. Looks like I am going to have to try to trace the cables to see what is in between. Are there any big caps or anything in there I need to worry about?

I still don't get how the thermostat is operating, though, since the manual says it requires 24VAC. Just bought the house a few months ago, so finding all these oddities is fun and aggravating!
 
  #14  
Old 03-01-16, 10:43 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,853
Received 1,477 Votes on 1,365 Posts
The red carries 24vac to the stat. The stat switches that red wire directly to the Y terminal for A/C or the W terminal for heat or the G terminal for fan.

The only thing that requires the C connection is the electronics in the stat itself. Most stats use batteries and don't require the C connection. Most old mechanical stats didn't require a C either unless it had a clock in it.
 
  #15  
Old 03-05-16, 07:52 AM
D
Member
Thread Starter
Join Date: Jun 2012
Location: USA
Posts: 9
Received 0 Votes on 0 Posts
Thanks! I'm going to try to trace out the wire today to see where and why it is splitting off.
 
 