How to wire Honeywell FocusPro 6000 to Infinity 96 System

my tenants broke the $700.00 Carrier Infinity Thermostat. I'm trying to replace it with the Honeywell as there is not a need for the Carrier anymore and can't get the wiring correct. can anyone guide me thru the process. thanks
 
  #2  
Old 05-23-16, 05:39 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,461
Received 83 Upvotes on 76 Posts
A furnace model number would be a more reliable number than the series number.
It is kinda like asking for the spark plug gap size of a Ford F150.


http://dms.hvacpartners.com/docs/100...TSTAT-13SI.pdf


It is possible that this is your manual. If this is the case move the wires from A,B,C,and D at the furnace to the conventional terminals.
The control wires at the outdoor unit would also need to be moved.

Some Infinity outdoor units do not support conventional thermostats.
Some Infinity furnaces do not support conventional thermostats.

Complete model numbers might allow us to look up the manual for you.

There is also more than one available FocusPro 6000.
The Honeywell TH6110 will not support a 2 stage outdoor unit.
You would need a TH6220.
 
 