Wiring info to replace Weathertron BAY28X139 with Honeywell RTH6350D

I'm trying to replace a Weathertron BAY28X139 with a Honeywell RTH6350D.

Weathertron has connections labelled:

R
T
O
G
Y
X2 jumpered to W & U
B
F

Honeywell has 2 identifications for each terminal:

Y2 - L
W2 - Aux/E
G - G
W - O/B
Not Used - Not Used
Y - Y
R - R
Rc - Rc

Documentation covers 3 ways of hooking up the Honeywell, none of which match.

Can anyone explain the correct way to hook up the Honeywell, or suggest a different replacement?

Thanks
 
Sponsored Links
  #2  
Old 05-30-16, 11:54 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,849
Received 255 Votes on 240 Posts
Welcome to the forums.

We need to know what color wires you have on which terminals.
A picture is ok. http://www.doityourself.com/forum/el...-pictures.html

The letters are not just matched between stats. Different stats assign different functions to different letters.

Name:  baystat.jpg
Views: 1334
Size:  37.0 KB
 
  #3  
Old 05-31-16, 12:55 PM
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 2
Upvotes: 0
Received 0 Votes on 0 Posts
Wiring photo

Name:  Weathertron.jpg
Views: 1358
Size:  20.4 KB
Note: - black had come adrift from F, so AUTO didn't work. Reconnected to F, and it AUTO worked.
 
  #4  
Old 05-31-16, 08:33 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,370
Received 10 Votes on 8 Posts
R = RC & R ( 24 volt power)
T = thermostat (Tape off this wire)
O = O/B (reversing valve to cool)
G = G (fan)
Y = Y (compressor)
X2 = Aux / E (heat strips)
B = C (tape off this 24vac common wire)
F = L (fault light) I would tape off this wire as well

F should not be able to control the fan. Could this have been a coincidence?

Remember to remove power to the indoor unit before replacement.
 
  #5  
Old 05-31-16, 08:47 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,849
Received 255 Votes on 240 Posts
I would have expected to see the black on X2.

Since you're in Md. ..... I'm sure your system has heat strips.
What may have happened is that heat and A/C was coming on at the same time.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: